Thread: Need Wiring diagram for TRUE TUC 60 F

  1. #1
    Join Date
    May 2006
    Location
    Amory Mississippi
    Posts
    1,012
    Post Likes

    Need Wiring diagram for TRUE TUC 60 F

    Naturally the wiring diagram that comes with the unit is long gone. Japanese restaurant so trying to see if the manager has it is fruitless. I'd prefer to have it before I start looking at that rats nest. I notice they use two temp switches instead of a standard defrost termination/fan switch. I tried the web site but it seems they don;t want just anyone looking at their technical data...

  2. #2
    Join Date
    Nov 2002
    Location
    PA
    Posts
    112
    Post Likes
    That unit should only have one temperature control and a defrost clock
    see link for manual, you can call them at 800-325-6152 and ask them to fax you a wiring diagram
    http://www.truemfg.com/CC_catalogs/t...rz_english.pdf
    If your not part of the solution, You must be part of the problem

  3. #3
    Join Date
    May 2006
    Location
    Amory Mississippi
    Posts
    1,012
    Post Likes
    Thread Starter
    it has one of those cheesy defrost timers like they use on cheap units. all plastic with 4 terminals the harness plugs into. There is one temp control on top of the evap and one on the suction line where it comes out of the evap. Each one has two wires. I'm guessing one is for defrost termination and the other for the evap fan. The evap fan is not running no matter how long the comp runs. I applied power and the fan is fine. No power going through the temp switch on the suction line which appears to be the evap fan control. A wiring diagram is always nice,
    I can take my meter and trace out all the circuits but it just takes longer. It would be nice if they glued diagram on the inside of the evaporator shroud. That's just me I guess.

  4. #4
    Join Date
    Mar 2008
    Location
    Atlanta(metro)
    Posts
    55
    Post Likes

    Thumbs up

    Quote Originally Posted by gsxrsquid View Post
    it has one of those cheesy defrost timers like they use on cheap units. all plastic with 4 terminals the harness plugs into. There is one temp control on top of the evap and one on the suction line where it comes out of the evap. Each one has two wires. I'm guessing one is for defrost termination and the other for the evap fan. The evap fan is not running no matter how long the comp runs. I applied power and the fan is fine. No power going through the temp switch on the suction line which appears to be the evap fan control. A wiring diagram is always nice,
    I can take my meter and trace out all the circuits but it just takes longer. It would be nice if they glued diagram on the inside of the evaporator shroud. That's just me I guess.
    usually the evaporator fan will not come on until the freezer temp drops (40-30f) so as not to circulate warm air throughout the box so you can check the t-stat circuit if the temp has dropped.

  5. #5
    Join Date
    May 2006
    Location
    Amory Mississippi
    Posts
    1,012
    Post Likes
    Thread Starter
    yep. that is what the switch is for. Usually I see a single switch with 3 leads. It does that same thing though. The evap frosts up, charge is good and it works fine if I jump the switch.

  6. #6
    Join Date
    Jul 2000
    Location
    Guayaquil, EC
    Posts
    14,652
    Post Likes
    On these units there are three temperature controls:

    1. Box temperature - (adjustable) senses discharge air temp and controls the compressor
    2. Fan Delay - (Klixon) mounted on top of the coil
    3. Defrost Limit - (Klixon) mounted on the evap outlet

    That cheap defrost control has four terminals:

    #1 > Hot
    #3 > Neutral
    #2 > Defrost Heaters
    #4 > Compressor/Evap Fan

    The drain tube and mullion heaters are energized constantly. That's about it.

    I had one similar last week...a TUC-27F...that had be going for a while. I had then fax me a wiring schematic which helped, but it's a ladder diagram and doesn't show the actual wire connections and routing, so tracing through the rat's nest of wires is a PITA.

    It turned out there was a broken neutral where the wiring came through the cabinet from the compressor compartment.

  7. #7
    Join Date
    May 2006
    Location
    Amory Mississippi
    Posts
    1,012
    Post Likes
    Thread Starter
    hmmmmmmmm I'll call and get the diagram. It's interesting because the fan switch on this unit was on the evap return and not on top of the evap. I wonder if someone else worked on it and switched them? hmmmmm
    thanks Ice

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •