    Geo sized too small at 70%

    There aren't too many geothermal installers in my area. The one I'm dealing with is recommending the 4 ton Climatemaster, even though it can only produce 37,500 BTU at full load, which is just over 70% of my home's heatloss (52,000 BTU). That sounds small to me. Can anyone help me understand if the system is properly sized?

  2. #2
    Join Date
    Jan 2004
    Location
    PA
    Posts
    68,773
    Does it meet the heat gain?
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  3. #3
    There is a line on the report that says "Avg. internal gains: 10,800 Btu/Hr" is that what you are looking for?

  4. #4
    Join Date
    Jan 2004
    Location
    PA
    Posts
    68,773
    Whole House 2,861.7 sq.ft. sensible gain 28,150 latent gain 8,810 total gain 36,960 heatloss 42,535

    Something like that.^^^^^^^
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  5. #5
    Here is the info I have from the report:

    Total Heated Area (inc bsmt): 3773 sq. ft.
    Total Building Heating BTU 52,925
    Total Cooling BTU BTU 36,885
    Sensible Cooling 28,401
    Avg internal gains 10,791

    Hopefully that is enough information to help you help me!

  6. #6
    Join Date
    Dec 2007
    Location
    oregon
    Posts
    885
    Quote Originally Posted by cleangreen View Post
    There aren't too many geothermal installers in my area. The one I'm dealing with is recommending the 4 ton Climatemaster, even though it can only produce 37,500 BTU at full load, which is just over 70% of my home's heatloss (52,000 BTU). That sounds small to me. Can anyone help me understand if the system is properly sized?
    what was your indoor design temp and outdoor winter design temp ( wetbulb)
    Genius = The guy who can do anything...except make a living!

  7. #7
    I'm not sure what a wet bulb is, but here are the design temps listed by the GeoDesigner program report I received.

    Winter design -2 deg F
    Summer design 84 deg F
    bld balance 57 deg F

    Winter Indoor 72 deg F
    Summer Indoor 75 deg F

    Delta T: 74 winter / 11 summer
    Summer daily range 22 deg F

    Hopefully the wetbulb is in that information.

  8. #8
    Join Date
    Mar 2007
    Location
    Connecticut
    Posts
    104
    Quote Originally Posted by cleangreen View Post
    Here is the info I have from the report:

    Total Heated Area (inc bsmt): 3773 sq. ft.
    Total Building Heating BTU 52,925
    Total Cooling BTU BTU 36,885
    Sensible Cooling 28,401
    Avg internal gains 10,791

    Hopefully that is enough information to help you help me!
    Where is the project located?

    My initial response for a heating dominated climate would be no, the unit is too small for your heat loss. The issue with Heat Pump sizing in conventionally built homes is you either size it for heating and it will be too big for cooling, or you size it for cooling and it will be to small for heating.

    In your situation the unit is appears to be a comprimise between the two. You will need to have supplemental heat (2nd or 3rd stage) to make up the difference during the colder weather. Again, if you live in a heating dominated climate, you want this part of the system operation to be efficient, otherwise it will cost too much and you loose the efficiency benefit of the heat pump. If you have gas hot water, you could add a hot water coil in the ducts to do this relatively affordably.

    If you choose to upsize your heat pump, you will need to have larger ducts, so this may be a limiting factor too (as to how big a unit you can connect to any existing ducts). Duct sizing is extremely important in getting heat pumps to operate correctly, so simply picking a larger heat pump may not actually get you any additional BTU's (plus it will be less efficient)!

    If you are in a cooling dominant region, then this system is fine, The amount of back-up resistance you use will be very affordable and there is no reason to complicate the design.

    PS - Ignore the average internal heat gains. That is not part of proper sizing routines for heating. It can be used for cooling, but is already accounted for in the peak calculations. That is something use to calculate energy consumption. We asked WaterFurnace to remove this fromtheir spreadsheet calculator 10 years ago when their dealers were running into problems here in the NE. WaterFurnace dropped the whoel spreadsheet and then ClimateMaster picked it up and used it in a stand-alone application they had developed. The proper way to determine loads is to use ACCA Manual J methods. It is independent of the sales spin any manufacturers wants to give. Once teh load is calculated, then you can decide what the proper piece of equipment is to satisfy the load conditions.

  9. #9
    Join Date
    Jan 2004
    Location
    PA
    Posts
    68,773
    That will give you a balance point of about 17*F.
    So around 19*F you would want your aux to come on with that match up.

    As above its been sized to the cooling load, plus 25%.
    Common for air to air heat pumps. (I realize your going geo)
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  10. #10
    Thanks everyone. I'm in Brampton, Ontario so we are certainly a heated dominated climate.

    Do you mean that at 19 defrees fahrenheit I would need to use the electric heat back up? That's only -7 degrees celsius, which is a good part of my winter.

  11. #11
    Join Date
    Jan 2004
    Location
    PA
    Posts
    68,773
    If your load calcs, and performace ratings are acturate.
    Yes, the HP would need the aux to come on with the HP to maintain stat set point at any temp under 17*F.

    Its common to bring the aux on 2*F before they are really needed to prevent eternal HP run time, and lose temp because of high winds.atleast on air to air systems)

    In Canada, they have their own load calc system which is rumored to be a bit more acturate then Manual J. Ask you contractor to use it, and see if it changes the load calc lower or higher.
    The more acturate the calc, the better equipment can be selected for the application.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  12. #12
    Join Date
    Jun 2006
    Location
    Lititz, PA (Lit' itz) not ( Li' titz)
    Posts
    122
    Is Guelph near you?

    I put that in geodesigner with your info

    Your balance point would be 13 degrees
    first stage heating 69%

    first stage cooling 100%

    aux heat require 5 KW

    full emergency 16 KW

    The geo will do about 96% of your heating with 4% back up

    This all figuring verticle bore with 1 inch pipe

  13. #13
    Join Date
    Mar 2003
    Location
    PA/DE area
    Posts
    1,535
    You guys make me PROUD!!
    It's NOT the BRAND,it's the company that installs it!!!!!

Page 1 of 3 123 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event