    These are flex duct connectors also.

    http://www.hartandcooley.com/flex/all_flex.htm
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  2. #28
    Join Date
    Dec 2003
    Posts
    709
    Quote Originally Posted by beenthere View Post
    Are you reading the code for flexable duct connectors.
    Or for flex duct.
    A flexable duct connector, is NOT flex duct. They are 2 different things.

    International Code says 14' for flexable duct connector.
    It has no limitation on flex duct.
    Dont think I understand your interpretation, please elaborate because the inspectors fail a job with more than a 14' run of flex.

  3. #29
    Join Date
    Mar 2008
    Posts
    657

    misread thread sorry!

    sorry guys, i thought the thread was about flex duct and not a flex duct connector. my bad

  4. #30
    Join Date
    Jun 2001
    Location
    Louisville, KY
    Posts
    12,181
    Quote Originally Posted by beenthere View Post
    These are flex duct connectors also.

    http://www.hartandcooley.com/flex/all_flex.htm
    That didn't work the way that you wanted.
    Perhaps you should have read the instructions before calling.

  5. #31
    Join Date
    Jun 2001
    Location
    Louisville, KY
    Posts
    12,181
    Quote Originally Posted by hivacer View Post
    Dont think I understand your interpretation, please elaborate because the inspectors fail a job with more than a 14' run of flex.
    Flexible duct pages 1-6.

    Flexible duct connector on page 7.

    http://www.hartandcooley.com/flex/flex%20catalog/Flexible%20Duct%20Systems%20Catalog%20-%20Edition%202.pdf

    Further reading...

    http://www.flexibleduct.org/ADC_FAQs.asp

    What is the difference between Air Ducts and Air Connectors?

    UL (Underwriters Laboratories), in their 181 Standard for Factory-Made Air Ducts and Air Connectors, defines two categories of flexible "ducts".

    The UL Listed Air Duct must pass all of the tests in the UL 181 Standard. Air Ducts are labeled with a square or rectangular shaped label showing their respective listing. There is no limitation on the length of runs when using UL Listed Air Ducts.

    The UL Listed Air Connector must pass only a limited number of the UL 181 tests, and is labeled with a round shaped label, which states "for installation in lengths not over 14 feet".
    Perhaps you should have read the instructions before calling.

  6. #32
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    67,909
    Thanks benny.


    hivacer.
    Your inspectors most likely don't know there is a difference between a flex connector, and flex duct.

    International Code limits flex connectors, not flex duct.

    Point out to them that they are two different things, they may change their mind.(do it politely )
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  7. #33
    Join Date
    Jun 2001
    Location
    Louisville, KY
    Posts
    12,181
    Quote Originally Posted by beenthere View Post
    Point out to them that they are two different things, they may change their mind.(do it politely )
    It's more fun to rub their noses in it.

    It's the little things in life that make me smile.


    Perhaps you should have read the instructions before calling.

  8. #34
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    67,909
    LOL..

    But your not the installer that has to face hiim again next week.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  9. #35
    Join Date
    Jun 2001
    Location
    Louisville, KY
    Posts
    12,181
    Quote Originally Posted by beenthere View Post
    LOL..

    But your not the installer that has to face hiim again next week.
    Ed Zachary!
    Perhaps you should have read the instructions before calling.

Page 3 of 3 FirstFirst 123

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event