    Return air - how close is too close to kitchen

    I am still working with my contractor to see what can be done to add another return air on the first floor of my home. A few weeks ago we were looking at trying to get something through my very shallow crawl space (I posted a question on that too).

    The only alternative to running it through the crawl, which will be difficult and somewhat expensive, is to have it near the kitchen in a mud room/pantry area right off of the kitchen. Virtually all the supply air that will be pulled through this return, except for the supply air in the mud room, will have the return path through the kitchen. I know it is not acceptable to have a return in the kitchen, but what about right outside of it and having the return path through the kitchen?

    My current setup has a single return at the back of the house and all the supply air from the front of the house and the mud room has to pass through the kitchen to get to the back of the house (kitchen is in the center of the house). This is the contractors argument stating that the new return really is no different with return air still passing through the kitchen, but this new return would be right next to the kitchen.

  2. #2
    Join Date
    Jun 2001
    Location
    DFW
    Posts
    684
    For a pratical - not according to code answer.
    put a smoke detector in your proposed location.
    burn some toast.
    It the smoke detector goes off, don't put the return air grill there.

  3. #3
    Join Date
    Sep 2006
    Posts
    1,253
    Quote Originally Posted by paul42 View Post
    For a pratical - not according to code answer.
    put a smoke detector in your proposed location.
    burn some toast.
    It the smoke detector goes off, don't put the return air grill there.
    Ha, we have a smoke detector high on the same wall and it goes off if we boil water. It must be a steam detector.

  4. #4
    Join Date
    Aug 2002
    Location
    Office and warehouse in both Crystal River & New Port Richey ,FL
    Posts
    18,836
    With the "open' floor plans we see in Florida the code officals want 10 feet between the exhaust fan and the return grille.Not "as the crow flies" ,so could be 5 feet in the kicthen and another 5 anround the corner and down the hall.

  5. #5
    Join Date
    Sep 2006
    Posts
    1,253
    Quote Originally Posted by dash View Post
    With the "open' floor plans we see in Florida the code officals want 10 feet between the exhaust fan and the return grille.Not "as the crow flies" ,so could be 5 feet in the kicthen and another 5 anround the corner and down the hall.
    I'm probably right at that.

  6. #6
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    67,776
    As Dash said 10' from range/hood.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?