    Unhappy Thermocouple Failure

    Does anyone know what causes thermocuples to fail? I have replaced 3 themocouples within 6 months on a standing pilot Weil McLain boiler. Any insight is appreciated.

    Doug

  2. #2
    Join Date
    Aug 2001
    Location
    Alberta, Canada
    Posts
    27

    Thermocouple issues

    Cast Iron boiler burner compartments generate very high temps. In situations like yours, sometimes a stainless steel high heat resistant thermocouple may give you more longevity. Penn-Johnson make one, and are usually available at Heating Wholesale. Also check btu firing rate of boiler...make sure you' re not overfiring.

  3. #3
    Join Date
    May 2006
    Location
    Rochester, NY
    Posts
    22
    If it's a continuing pilot outage problem...
    Are you sure the T-couple is at fault? Have you checked the DC millivolt reading before replacing the T-couples?

  4. #4
    Join Date
    Mar 2008
    Location
    albany, new york
    Posts
    20

    Lightbulb thermocouple

    make sure no part of thermocouple is touching anything metal.

  5. #5
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    67,765
    Improper set up.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  6. #6
    Join Date
    Nov 2001
    Location
    east kansas
    Posts
    8,024
    Where in Alsaska are you?

    I was at Ft. Greely for a while. Spent a lot of weekends in Fairbanks.
    Beware of advice given by some guy on the Internet.