More for you think about....has anyone checked your airflow properly using a monometer and a blower chart?? 90% of all systems have improper air flow and until that issue is resolved....your refergerant charge will never be correct.
I need a new signature.....
if its is checked by superheat, then fine. if it needs to be "charged" by superheat, then get the leak fixed and you won't have to worry with it for a while
If Guns Kill People, Do Pencils Misspell Words?
http://www.youtube.com/watch?v=An2a1...eature=related
Before we work on artificial intelligence why don't we do something about natural stupidity?
1) A 13 SEER American Standard would utilize a TXV and would require the subcooling to be tested for system charging.
2) This system has a factory installed drier and would not require an external drier.
3) You do not need to check the charge at every preventive maintenance to perform it correctly. Why do you want to remove refrigerant every year when removing your 6' hoses? Take the time to verify and maintain airflow. The air conditioner is a sealed system and will not require refrigerant unless a leak is present.
How would you know if a leak has developed without checking the superheat / subcool on every inspection?? I do and will check charge EVERY time...the point of PREVENTATIVE MAINTENANCE is to catch possible problems before they have time to develope.
Also...just because you have a TXV doesnt mean that you shouldn't check your superheat...with it, you are only doing it half-azz...superheat can tell you alot about a system....ESPECIALLY one with a TXV.
Spent the extra time on a call today....just a PM and found that the system was low on charge....will be returning on Monday to find the leak....and by the way....as of August of last year...the unit was working perfectly....now...do you think that the homeowner was glad that I checked the superheat today????
I need a new signature.....
If Guns Kill People, Do Pencils Misspell Words?
http://www.youtube.com/watch?v=An2a1...eature=related
Before we work on artificial intelligence why don't we do something about natural stupidity?
I was not trying to be funny my experence is you cannot have the perfict charge when servicing at low outdoor ambent temps.
I need a new signature.....
The reality is that once a system has been installed you do not need to place a set of gauges on it to check superheat or subcooling unless you are less than confident in your brazing and leak test abilities.
Confirm your airflow is 400 CFM per ton and perform a calculation of the installed total capacity(Measured CFM X 4.5 X Delta Enthalpy). Once you benchmark a systems capacity at installation it is very easy to determine when a future problem arises.
This works as long as the system is tested under similar conditions in the future. Same airflow, not diminished by dirty coils/filters/blower wheels, same outdoor temperature, same indoor heat load, same indoor wet bulb. Otherwise, there will be variance from the initial capacity check. Perhaps not significant deviance, but the only time a system is said to be operating at rated/nominal capacity is when it is under ARI rating conditions, which are 95 degrees outdoor dry bulb, 80 degrees indoor dry bulb, 67 degrees indoor wet bulb. Since many of us prefer 75 degrees dry bulb and 55 or lower degrees indoor wet bulb, the actual operating capacity, even when outdoor ambients are at 95, will be other than nominal.
For the OP, I must agree with others who have stated the evidence you've presented so far...a technician with a mostly upside-down refrigerant bottle being startled upon your arrival...is not enough to assume your system has an incorrect charge. Personally, if I were concentrating on charging your system properly and you came up behind me without making much sound, I might jump with a start as well once I realized you were there. It's just a natural reaction to the unexpected.
I don't lose any freon checking the charge. Always empty the hoses back in to the low side before pulling them loose. The quantity of refrigerant vapor left in the hoses will be absolutely insignificant. If the set doesn't leak, then it will even be less than insignificant because the static pressure in them will be about the same when you leave as it was when you got there.
Benchmarking is good for factory engineers. Not good for resi service. We don't have time to wait for indoor and outdoor conditions to repeat themselves, and when these are different capacity is also different. Capacity isn't a constant, not by a long shot. I have a chart and a slide rule, either of which will determine whether air volume is in the correct range as long as the charge is ok, but you have to confirm a proper charge before using it.
Charge is more critical than air volume, and it is difficult to accurately measure air volume to the precision required for you to determine charge levels by differences in enthalpy. If your calculation is only very slightly off, then you could lose a compressor because you didn't do something as simple as check superheat.
Last edited by hvacrmedic; 03-15-2008 at 01:40 AM.
OP: I guess since that was a joke that meant more to the people in the trade, I guess that's why I didn't get it. --Sorry!
I appreciate hearing all the techs say that doing a superheat & subcooling check is part of what they'll do as part of a PM. That's exactly what I wanted to hear - of all the people I've had out over the years, none have done a superheat / subcooling calculation.
Now I just need to find just such a firm to do my PM.
Twilli says whats superheat, we don't need that on Colemans
No Heat No Cool You need Action Fast
Your system has a TXV for its metering device. The correct charge is determined by subcooling. The superheat still needs to be checked to verify that there are not other refrigerant circuit related problems though.
Depending on the model, your system has 1 or 2 factory installed liquid line filter driers inside the unit, there should not be one installed outside the unit.
Many people charge a system with the refrigerant bottle turned upside down, and either throttle the refrigerant in with the valve on the refrigerant manifold, or use a small device that goes inline with a refrigerant hose that insures the liquid flashes off before it makes it to the system.
You walked up behind a guy, who had his attention focused on something else, and you are concerned that he was startled when you said something?
I do understand your concerns though.
Only a very small percentage of installers and service techs actually flow nitrogen through a system when brazing the refrigerant lines. This despite it being a specific requirement in virtually every manufacturers installation instructions.
Only a minority of installers/techs who actually use a micron gauge during evacuation, again, this is despite clear manufacturers instructions regarding vacuum level requirements.
Depending on who's study you look at, between 56% and 73% of newly installed systems are incorrectly charged at startup, most by more than 10%.