    I need help with a Carrier Roof/Top unit...Please

    Hi All… I am Dave

    Really could use your help... I am a certified A/C and Heating Technican... I graduated from RSI, (Refrigeration School Institute),Institute in Phoenix.. I am asking for a second opinion of which the first is my opinion... But I need your help if at all possible...

    I have a Carrier roof top, A/C and Heating unit that has a Mother Board or called a control Board... This board has an Error code detection light when something is wrong... It flashes 1 thru 8 error codes.... Now the particular errors are as follows... It listed 3 errors...
    The inducer fan will not shot off to complete the shut down cycle after it reaches the Thermostat setting…. As the fan just keeps running until I turn off the main power and these are the error codes that are displayed on the Board before I shut off the main power…

    1 flash.... Fan on/off delay modified
    6 flashes.. Inducer switch fault
    8 flashes.. Internal control fault

    I have never had a unit show so many errors codes... But my opinion is that the Mother Board,(Control Board),is at fault and I need another Mother Board, (Control Board). Because the Fan Delay is internal to the board and also the Internal Control Fault is also part of the Board, and I also believe that the Inducer Control switch is also part of the board.... Can you confirm that I need a new board??? I do not want to replace the board with out a your advice first....

    Carrier Roof Top... A/C n Heating unit

    Model #..... 48SS-042080321
    Serial #.... 4695G80613

    Thank You,
    David Morton...

  2. #2
    Join Date
    Jul 2005
    Posts
    5,509
    Code 8, internal control fault = defective board. Usually.

  3. #3
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    67,900
    Provided you checked to make sure no one has put a power stealing stat on that unit. And that voltage is proper.
    Code 8 usually means the board is bad.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  4. #4
    Thank you very much for your information..... Never had a unit show this many faults at once.... So I was second guessing my self.... Again thank you.... and I will let you know how it goes when I get back to that unit..... This is what I was thinking that the board was bad.... But needed a second opinion....

    David Morton

  5. #5
    Thank you very much for your information..... Never had a unit show this many faults at once.... So I was second guessing my self.... Again thank you.... and I will let you know how it goes when I get back to that unit..... This is what I was thinking that the board was bad.... But needed a second opinion....

  6. #6
    Join Date
    Jan 2005
    Posts
    5
    Before you go to a new board, take off ALL t-stat wires & just jump out R&W & see if there are errors on a call for heat..

    If not, then you can focus on the t-stat.

  7. #7
    Join Date
    Jan 2006
    Location
    Hangin out with you losers
    Posts
    1,043
    Chek your high voltage
    I had a loose connection that was melting the wires inside of the disconect
    the unit ran but the board gave me a mess of codes as well
    I remember my first day,It was fun!

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event