Results 1 to 10 of 10
    Ohio
    Flue Gas Condensing Temperature
    As I am now dealing with a job that has Lochinvar CHHN0990 non-condensing boilers that were condensing in the boiler as well as the flue, I've done a little search and found that natural gas flue gas condenses at 60*C, which equals 140*F. Coincidentally, that is the minimum allowable return water temperature to these boilers. Return water less than 140* is no longer a problem.
    As I have seen a lot of white crusty evidence of condensation on the flue where the flue goes thru an unconditioned/ventilated attic, would it be proper to assume the flue gas was/is dropping to 140* in this section? And to prove it, I want to test the flue gas temp at this point.
    Does this make sense?
    Anybody have experience with this?
    BTW, both boilers, and the Lochinvar domestic boiler show the same condensation evidence.
    jogas
    birmingham, al
    had the same problem with a raypak boiler, on a water source heat pump loop. My boiler was severely condensating, entering water temp was too low and boiler tubes were sooted. I had to replace 10 out of 17 burners,refactory, both igniters, flame sensors,and front plate. raypak states return water temp must be 105* or greater in 7 minutes. had to change how boiler was being controlled by ems and ajust bypass.
    WI
    Chances are, the boilers are underfired. Set it up with a combustion analyzer and make sure the draft and flow rate is ok. Flue gasses condense at temps much warmer than 140. You should see flue temps of around 400* to 500* for nat gas.
    Ohio
    Quote Originally Posted by DesMech View Post
    I realize that, at the boiler outlet, but 25' up, thru 4-6 45* el's, where it travels thru a ventilated attic, the flue gas temp drops way off.
    See attached attic flue pic.
    jogas
    Mar 2001
    Pix don't work. If I remember right, under 350F will condensate flue gases. You may need to insulate the vent or change it to an insulated type ('A' vent) to protect the temperature. (possible power vent or assist?)
    oc
    water temp may still be an issue most new boilers are using a pid control
    which recirculates the hot water back into the boiler to help prolong the boiler .
    Mar 2001
    Now the pix work. You may want to drop a scope down that vent to check the integrity of the flue liner.. looks like 'B' vent... al. liner may be damaged.
    WI
    Quote Originally Posted by jogas View Post
    jogas
    Do you have combustion and draft readings?
    Apr 2002
    Quote Originally Posted by ersham View Post
    even some condensing boilers with drains will use a mixing valve. the WM GV series used to have a mixing valve built right into them
    Ohio
    We are going to use a sewer drain camera to drop down each flue to determine the condition of the inner wall, which is class 1 (galvanized). No sense going any further if the flues are rotted. Been this way since '02.
    There's another 150M domestic water Lochinvar that is also condensing badly.
    I'm thinking about gathering the 2- 990M's and the 150M and using a modulating Exhausto style induced draft setup.
    Anybody had any good/bad experiences with them?
    I've got the return temp problem solved. 2 DDC loops, one looks at return temp, the other looks at each boiler's supply as a high limit. Working well so far.
    jogas