    Question American Standard 5 ton condenser with 4 ton air handler

    I got a quote for a HVAC replacement. The dealer wants to install a 5 ton condenser 2A7A8060B with a 4 ton air handler 2TEE3F49A due to space restrictions in the closet. According to ARI standards this will give 58500 Btuh, an EER rating of 10.80 and a SEER rating of 16.50
    Is this mismatch in tonnage OK? I am a little worried since I thought tonnage should be the same.
    Please help

  2. #2
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    33,897
    You're fine. You lose 500 BTUs and .75 SEER point over the 065 but this is an approved match and if it fits better, should be the way to go. Pretty rare that a system gets the exact capacity.

  3. #3
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    67,721
    If it has an ARI rating, no problem.
    Since its all A/S equipment, they tested it.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  4. #4
    Join Date
    Aug 2004
    Location
    North Richland Hills, Texas
    Posts
    14,914
    AS/Trane has more than 10,000 ARI listed equipment combos, some of them are even stranger sounding than what your proposal has.

    They used to have a couple with a 5 ton straight AC outdoor unit matched with a 3.5 ton indoor coil, with 1600 cfm through the indoor coil.
    If more government is the answer, then it's a really stupid question.

  5. #5
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    6,238
    Quote Originally Posted by Manny View Post
    I got a quote for a HVAC replacement. The dealer wants to install a 5 ton condenser 2A7A8060B with a 4 ton air handler 2TEE3F49A due to space restrictions in the closet.

    According to ARI standards this will give 58500 Btuh, an EER rating of 10.80 and a SEER rating of 16.50

    Is this mismatch in tonnage OK?
    Yes.

    Good match for a humid area where
    air flow should be set at ~ 350 CFM/ton.

    See page 9 of the TRANE AHU attachment.
    Attached Images Attached Images
    Designer Dan
    It's Not Rocket Science, But It is SCIENCE with "Some Art". ___ ___ K EEP I T S IMPLE & S INCERE

    Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities

  6. #6
    Join Date
    Dec 2006
    Location
    Middle Tennessee
    Posts
    11,347

    *

    Quote Originally Posted by Manny View Post
    I got a quote for a HVAC replacement. The dealer wants to install a 5 ton condenser 2A7A8060B with a 4 ton air handler 2TEE3F49A due to space restrictions in the closet. According to ARI standards this will give 58500 Btuh, an EER rating of 10.80 and a SEER rating of 16.50
    Is this mismatch in tonnage OK? I am a little worried since I thought tonnage should be the same.
    Please help
    if i am not mistaken that 49A variable speed air handler will match up with 3-1/2 thru 5ton condensers

    dip switches will need to be set accordingly



    .

  7. #7
    Join Date
    Nov 2007
    Posts
    4
    Thank you all for your replies. Very helpfull to me.