03-22-2008, 09:46 PM #80
The Blue guage. Is the compound guage. Its the guage that belongs on the low pressure/vapor line. It shouldn't be at 160PSI when the system is running. If its on the vapor service port.
He may have had it on the liquid line.
Did he have both lines hooked, or just one.
He guessed at how much to take out.
-
03-22-2008, 10:27 PM #81
Professional Member
- Join Date
- Feb 2007
- Posts
- 190
-
03-22-2008, 10:59 PM #82
Regular Guest
- Join Date
- Nov 2007
- Posts
- 23
You are correct - I got the gauges mixed up, the RED gauge read ~160psi and the BLUE gauge read ~64psi. I was going off of memory and had to go back and look at the picture I took of the gauges.
He measured the weight of the refrigerant on a digital scale and took out when the pressures dropped with in the specs on the service charts. At first the red gauge was reading over 400psi when in heat pump mode which gives off a higher psi value compared to A/C mode. According to the Trane Rep it is more accurate to test pressures in A/C mode.
Thanks again for all your input and I'll keep you posted on what comes of the line-set noise.
K
-
03-22-2008, 11:10 PM #83
Yes, it is.
He should have recovered the charge. Measured the line set, and then weighed back in the amount the line set length needs.
-
03-22-2008, 11:33 PM #84
Regular Guest
- Join Date
- Nov 2007
- Posts
- 23
-
03-23-2008, 07:15 AM #85
7', they needed to remove charge when they installed it.
-
03-23-2008, 11:44 AM #86
Professional Member
- Join Date
- Feb 2006
- Location
- Tn.
- Posts
- 1,331
-
03-23-2008, 11:54 AM #87
-
03-24-2008, 12:56 PM #88
Professional Member*
- Join Date
- Aug 2007
- Location
- Northern VA 38 degrees N by 76 degrees W
- Posts
- 3,251
-
03-25-2008, 12:27 PM #89
Regular Guest
- Join Date
- Nov 2007
- Posts
- 23
-
03-25-2008, 03:13 PM #90
New Guest
- Join Date
- Mar 2008
- Posts
- 2
Recover vacumm and measure
Stop playing around with this customer. Recover. Vacumm. Measure Line length and rise. Wiegh in. Come back when the temp is warmer? Who does that, I agree Trane tech should not leave until problem is resolved. Home Depot & Trane = 100% Customer Satisfaction. I would be pissed if I were this contractor, Once had XL19i 5ton loose a compressor a week after install, tested for acid in the system, had both new compressors in the next day! Homeowner has every right at this point to contact Home Depot and Trane and demand another contractor that knows what he is doing. If you don't know how to install it than don't sell it.
-
03-25-2008, 03:40 PM #91
Professional Member*
- Join Date
- Aug 2007
- Location
- Northern VA 38 degrees N by 76 degrees W
- Posts
- 3,251
your dip switches are set up for 450 cfm for 3.5 tons. you have a 3 ton. 5/6 are set for 1.5 min. delay on cooling 7/8 are on medium heat.



Reply With Quote
This sound still bugs me and to me is considered NOT normal for a top of the line unit - it really is noticeable and is more apparent when the Heat Pump on but less noticeable when the AC is on. This must be due to the increase of pressure when the HP is operational vs the AC.
,