York Chiller Lock-out
Hey, we ran into a situation where a ~100 ton York chiller locks out after a power outage.
My thought is that it would be the staring relays are bad, but when the York techs looked at it they didn't say anything about it and couldn't solve the problem.
Anyone else get around an issue like this?
-
03-05-2008, 02:40 PM #2
units running?and you lose power that's a latching lock out and the alarm off the panel has to be reset/cleared to restart
"when in doubt...jump it out" http://www.youtube.com/watch?v=aMy-sAHwS4E
-
03-05-2008, 02:52 PM #3
******
"when in doubt...jump it out" http://www.youtube.com/watch?v=aMy-sAHwS4E
-
03-05-2008, 06:28 PM #4
I agree w/ Maxster, there is most likely some kind of phase protection going on where the unit will not start w/out being reset @ the control panel, after a fault, regardless if the start/stop switch is closed or not. What's the model of this chiller?
Sic Semper Tyrannis.
-
03-05-2008, 07:07 PM #5
Professional Member
- Join Date
- Nov 2005
- Location
- Shreveport, Louisiana
- Posts
- 2,240
-
03-07-2008, 10:37 PM #6
Professional Member
- Join Date
- May 2006
- Posts
- 60
check all sensor for that unit,,
juan clavell santiago
-
05-01-2008, 06:26 AM #7
Regular Guest
- Join Date
- Sep 2007
- Posts
- 16
model # ???
-
05-01-2008, 12:05 PM #8
Member
- Join Date
- Sep 2007
- Location
- Yuma, Arizona
- Posts
- 252
Perhaps the programming needs to be set up for an automatic restart???
But I highly doubt the York guys overlooked something as simple as that!
-
05-02-2008, 10:17 PM #9
Professional Member
- Join Date
- May 2004
- Posts
- 122
What are you reseting??? the control panel or the overloads?? if its the latter, Ive installed ICM 450 phase?voltage monitors to shut machines down before a manual reset is required.