Results 1 to 9 of 9
    York Chiller Lock-out
    Hey, we ran into a situation where a ~100 ton York chiller locks out after a power outage.
    My thought is that it would be the staring relays are bad, but when the York techs looked at it they didn't say anything about it and couldn't solve the problem.
    Anyone else get around an issue like this?
    Oct 2001
    units running?and you lose power that's a latching lock out and the alarm off the panel has to be reset/cleared to restart
    "when in doubt...jump it out" http://www.youtube.com/watch?v=aMy-sAHwS4E
    Oct 2001
    Oct 2006
    Central Texas
    I agree w/ Maxster, there is most likely some kind of phase protection going on where the unit will not start w/out being reset @ the control panel, after a fault, regardless if the start/stop switch is closed or not. What's the model of this chiller?
    Sic Semper Tyrannis.
    Nov 2005
    Shreveport, Louisiana
    Quote Originally Posted by maxster View Post
    BINGO
    UA Local 141
    check all sensor for that unit,,
    juan clavell santiago
    model # ???
    Yuma, Arizona
    Perhaps the programming needs to be set up for an automatic restart???
    But I highly doubt the York guys overlooked something as simple as that!
    What are you reseting??? the control panel or the overloads?? if its the latter, Ive installed ICM 450 phase?voltage monitors to shut machines down before a manual reset is required.