Not sure about furnace size
The space being heated is about 5,000 square feet, 2,500 on the first floor and 2,500 in the basement. In the basement only 1,200 square feet is finished.
The following specs were taken from HVAC plans.
Heating Specifications
Heat Loss 87715 BTUH
Equip Manufacturer Carrier
Gas furnace model 58STA135-22
Gas furnace input 132,000
Gas Furnace output 107,000
Gas furnace AFUE 80.0
Rated CFM 1715
Air Temp Rise 57
Cooling Specifications
Heat Gain 53181 Total BTUH/43683 Sensible
Equip Manufacturer Carrier
Condenser Model 24ABA3060A30
Evaporator Model CNPVP6024ACA
Net MBH Total 57.0
Net MBH Sens 44.1
SEER Rating 13.0
Rated CFM 1420
Given the above, will a comfort 92 model 58MXB080-20 do what the basse model 58STA135-22 does in regards to heating this space? This is all the info I have.
-
03-03-2008, 09:29 PM #2
At 87K heat loss it may end up a bit shy on extremely cold days, but depending on the "fudge factor" of the load calc program, you may be in good shape.
Who did the load calc?You can't fix stupid
-
03-03-2008, 10:56 PM #3
Regular Guest
- Join Date
- Oct 2007
- Location
- Washington, DC Metro Area
- Posts
- 14
"Who did the load calc?"
The HVAC company. It is a large local company. Not sure I should mention their name. I thought the furnace was going to be a 58MXB120. However, I did not get the furnace size in writing. By the way, this is new construction.
Wha's the rule of thumb, furnace output, in this case 77,000 BTUH?, should be equal to or greater than the heat loss 87000 BTUH?
-
03-03-2008, 11:10 PM #4
Well based on the load calc, I would say it is undersized, but to me a 2,500sq ft home for most cases an 80K btu 92%er would be great plenty, if they did the load calc wrong (say they inputed the wrong stuff for the below grade space) the calc would come out higher. If they are a large reputable company, then give it a shot, if it can't keep up in sub zero weather, they should back it up and change it out. They did the calc and feel comfortable with their decision to go smaller so give them the benefit of the doubt, they are the pros. Lower BTU's for the most part will cost less to operate, oversized equip that short cycles cost you more to run, and 95% of the yr the equip would be oversized, at the most you would need a 100K not a 120K
You can't fix stupid
-
03-04-2008, 02:50 AM #5
Professional Member*
- Join Date
- Nov 2004
- Location
- SW FL
- Posts
- 5,270
Designer Dan
It's Not Rocket Science, But It is SCIENCE with "Some Art".

Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities
-
03-04-2008, 05:59 AM #6
Regular Guest
- Join Date
- Oct 2007
- Location
- Washington, DC Metro Area
- Posts
- 14
Thanks.
-
03-04-2008, 07:32 AM #7
For new construction, the calcs sound high.
Must have a lot of glass.