Have your engineer look at the building diversity and see if there is enough to reduce the size of your outdoor unit. If not then you will need the full 84K BTUs. Have not heard yet what your heat loss is. How does it compare to your cooling load?
1. The 130% figure does not mean that the outdoor unit can overrun by 30%, although it can produce a little more when 130% is connected as compared to 100%. It means that the total total capacity of the indoor units combined can be as high as 130% of the outdoor. That number on the newest models is moving up to 150% and 200%. This allows you to size the indoor units such that one part of the building may need at or near full capacity as will another part of the building - just not at the same time (diversity).
2. Efficiency is about the same between the larger sizes and the smaller ones.
3. Yes, some manufactures will use two smaller compressors and others one compressor. When there are two, one is an inverter driven compressor and the second a fixed speed compressor. The system determines when one, or the other, or both run.
4. The more sophisticated PC based controls may be able to incorporate that feature.
5. Have not researched the ERV/HRV differences. Most all can incorporate them within the system though.
-
03-09-2008, 06:10 PM #15
Regular Guest
- Join Date
- Mar 2008
- Posts
- 11
Heat 95k...is that what you wanted to know?
-
03-09-2008, 07:48 PM #16
Regular Guest
- Join Date
- Sep 2006
- Posts
- 1,253
Yes, thanks.
The sizing is generally as follows, but may be a little different depending on the manufacturer:
Cool/Heat (in 000's BTUs)
36/40
48/54
72/81
96/108
Sanyo does not have a 48/54 but rather has a little larger 53/60. Thus, depending on whether you can use a smaller unit because of diversity, you may decide to go with a two smaller single phase systems such as the 36 and 48. The 36 can have six indoor units and the 48 eight. Diversity may be able to bring you down to the 72, otherwise, you may have to go a little oversized (one ton) and use the 96 (it will help when you have those larger summer gatherings and temporarily increase the load). The 72 and 96 are three phase systems.
In any event, you will still be able to have a central control system that will interface with the outdoor unit(s) and all the indoor units.
-
03-09-2008, 07:54 PM #17
Regular Guest
- Join Date
- Sep 2006
- Posts
- 1,253
I think the manufacturers have increased the training and have a minimum tool provision. Hack saw has been replaced with a sawsall (cordless optional), gauges not dating farther back than the mid `70's, and duct tape on the job site is always good to see. ;>) Things are looking up.