03-06-2008, 08:49 AM #28
You are right, it has 2-stage hp and 2-stage gas. However, the manual states that the factory configuration is for high fire only. I don't know if the installer has changed this, but I doubt it.
I've wondered about the refrigerant. This is a packaged unit, so it came pre-charged - it should be ok? The installer told me that he could not check the refrigerant until the outdoor temperature is warmer (above 70 I think he said).
Ok, enough with the acronyms.
What is FR?
The installation manual states the following: "The ducts must be properly sized not to exceed .2" w.c. pressure drop at 400 scfm per nominal ton of cooling capacity."
It is a 5-ton system, so does that mean the total pressure drop should not exceed 1" w.c. at 2000 scfm?
What is w.g.? How does it compare to water column?
I wish I had a motor performance chart for my blower. It is not in the installation manual.
The M1200 installation manual shows the ambient sensor mounted in a little metal box screwed to the side of the unit right next to an exhaust vent. The metal box is nowhere to be found (must have been discarded at installation). Maybe it would work better if I fabricated a box for it?
Sorry for all the questions. I'm learning as fast as I can.
Thanks
-
03-06-2008, 08:53 AM #29
-
03-06-2008, 08:57 AM #30
Banned
- Join Date
- Aug 2002
- Location
- Office and warehouse in both Crystal River & New Port Richey ,FL
- Posts
- 18,836
-
03-06-2008, 10:20 AM #31
FR stands for friction rate.
WC, water column.
No, .2" wc at 400 CFM per ton still means .2" wc total for a 5 ton unit moving 2000 CFM.
Look around the duct system. See if you see air leaks where thsy are attached to the new unit.
Might want ot check the ducts in the crawlspace for insulation falling off, and for air leaks also.
-
03-10-2008, 09:43 AM #32
Return restricted by design?
I talked to my contractor about the returns. When I expressed concern that the hole in the floor was too small (actually less area than the 16" duct), he said that if it were made larger, then the system would pull less from the other return, and we don't want that.
http://www.hvac-talk.com/vbb/attachm...3&d=1204557642
-
03-10-2008, 11:33 AM #33
It may pull alittle less from the other return.
The combined total will still be greater then what you currently have.
Poor excuse.
-
03-10-2008, 11:56 AM #34
Banned
- Join Date
- Aug 2002
- Location
- Office and warehouse in both Crystal River & New Port Richey ,FL
- Posts
- 18,836
Although you have a VS motor it has limits on how restrictive the ducts can be,and still deliver the required air flow.
Your return ducts are almost certainly undersized,wondering what the supply is sized like.
Higher static(think resistance) is costing you more then normal to operate the fan,and will continue to do so until it's corrected.
Ask your contractor to seek some help from his distributer,they likely have the ability to test the static ,and maybe help design remediation of the duct system.If not they need to find someone to assist them.
-
03-10-2008, 09:02 PM #35
Look for a contractor on this site.
http://nationalcomfortinstitute.com/
They can help you.Read, read, read!
-
03-11-2008, 04:28 PM #36
I think we're making progress
After discussing the issues with my contractor (using much of what I have learned from this forum), he spent all day working on the system. Here is what he reported:
- He has enlarged the hole in the floor, and says the air flow has increased significantly. He says the esp (he found his manometer!) was .28 and he got it down to .11 after cutting the hole larger. Tomorrow he plans to replace the 20x25 grill with a 24x30.
- He installed dampers in most of the branches and used hoods to measure/balance the air flow to each room.
I am hoping we are on the right track here. Thanks to all for the advice.
-
03-11-2008, 04:36 PM #37
IS that in first stage, or second stage.
Was that the return static, or the TESP.
-
03-11-2008, 04:44 PM #38
-
03-11-2008, 05:03 PM #39
Banned
- Join Date
- Aug 2002
- Location
- Office and warehouse in both Crystal River & New Port Richey ,FL
- Posts
- 18,836
.28 is low,if it's the total of the supply and return.
Ask where he took his readings.
It should be as close to the supply and return air takeoffs at the package unit as possible.




Reply With Quote
.