    DX-9100 PID module

    Hello

    The PID program Module on a DX 9100

    I want to use the value stored in the connected ACO 1 as the remote setpoint for the PID module

    I f the value in ACO 1 = 72 then that is what I want the PID setpoint to be.


    Do I have to change the Local Setpoint value to Zero in order to do this?
    Thank You

  2. #2
    yes, whatever is in the local would be added or subtracted to it. So zero would be the aco value only.

  3. #3
    Join Date
    May 2006
    Posts
    22

    Remote setpoint

    If you want to disable the local setpoint completely, change the remote mode to a 1, any local setpoint adjustment will be ignored.