    Jul 2002
    NorthEast
    DX-9100 PID module
    Hello
    The PID program Module on a DX 9100
    I want to use the value stored in the connected ACO 1 as the remote setpoint for the PID module
    I f the value in ACO 1 = 72 then that is what I want the PID setpoint to be.
    Do I have to change the Local Setpoint value to Zero in order to do this?
    Thank You
    Mar 2006
    yes, whatever is in the local would be added or subtracted to it. So zero would be the aco value only.
    Remote setpoint
    If you want to disable the local setpoint completely, change the remote mode to a 1, any local setpoint adjustment will be ignored.