fujitsu
Is there a way to check to see if the charge is right on a multi zone 24rmlq other then weighing the charge?
-
02-29-2008, 05:19 PM #2
Regular Guest
- Join Date
- Sep 2007
- Posts
- 48
good questuon curious about that also
-
02-29-2008, 05:34 PM #3
Professional Member
- Join Date
- Nov 2006
- Posts
- 523
Turn on both units, cooling, fan high, test run. Should start flashing red & green continuously and blow cold. Pressure should read 116-118
-
02-29-2008, 07:32 PM #4
Weigh it in, this is the only correct way to check charge.
Karst means cave. So, I search for caves.
-
02-29-2008, 08:38 PM #5
Professional Member
- Join Date
- Feb 2007
- Location
- 18951
- Posts
- 1,593
-
02-29-2008, 09:22 PM #6
Professional Member
- Join Date
- Nov 2006
- Posts
- 523
You shouldnt have to weigh in any charge on a dualzone 24rmlq as it comes precharged from the factory for the maximum lineset length. As for oil return, that shouldnt be a problem because the only thing traveling through the pipes is gas and some atomized oil. The expansion device is located on the outdoor unit and both pipes are on the low side of the system, which is why they both need to be insulated seperately.
-
02-29-2008, 09:31 PM #7
Regular Guest
- Join Date
- Sep 2007
- Posts
- 48
installed one this week pretty cool that both lines are on low side of system took awhile for some guys to understand that.so if my line set is 15' or 30' the charge in the condenser will be o.k.