Thread: Aux elect heat cycles
-
02-28-2008, 09:13 AM #1
Regular Guest
- Join Date
- Jan 2008
- Location
- Lehighton, Pa.
- Posts
- 171
Aux elect heat cycles
Have a Lennox x16 HP, var. speed, Harmony III system. Last night the outdoor temp was 27 deg. Based on the Led's on the Harmony board the aux elect. was bouncing between first and second stage.
Question: Is it normal for aux heat to kick in while having 27 deg. outdoor temps?
-
02-28-2008, 12:00 PM #2
It depends on many things.
Its common on some systems. And others won't use aux until it gets even colder.
-
02-29-2008, 05:14 AM #3
Professional Member*
- Join Date
- Nov 2004
- Location
- SW FL
- Posts
- 5,262
27'F range seems to be a common balance point.
2 stage Heat Pump should be on 2nd stage for a while prior to aux heat.
Your wording may need clarification.
You may wish to lock out electric heat strips (aux heat) at > about 22'F,
if you wish to conserve energy.
How is the heat pump defrost operation in your area at < 30'F?Designer Dan
It's Not Rocket Science, But It is SCIENCE with "Some Art".

Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities
-
02-29-2008, 07:50 AM #4
Regular Guest
- Join Date
- Jan 2008
- Location
- Lehighton, Pa.
- Posts
- 171
With the Harmony board there is a four minute delay between all four stages if called for. Four stages meaning two for the HP and two for the back-up elect.
There doesn't appear to be a lock-out function based on temperature for this unit.
This unit handles the defrost function by using various sensors to determine when to activate the defrost. It is not like most units that are activated strictly using a timer. I don't necessarily have a problem with the strips running. I was just questioning if it should operate that way.
Thanks for your response.
-
02-29-2008, 11:12 AM #5
Your aux heaters could cycling on a bonnet sensor.
-
03-01-2008, 12:02 AM #6If Guns Kill People, Do Pencils Misspell Words?
http://www.youtube.com/watch?v=An2a1...eature=related
Before we work on artificial intelligence why don't we do something about natural stupidity?
http://www.youtube.com/watch?v=nFl0n...ture=endscreen
-
03-13-2008, 06:40 AM #7
Regular Guest
- Join Date
- Jan 2008
- Location
- Lehighton, Pa.
- Posts
- 171
Here's an update to my original question. Today, outside temp 48, stat set to 73. With one zone running, the unit ramps up to first stage aux. Another zone then calls for heat and unit ramps to second stage aux.
The aux is 10 kw. Now, with the outside temp being 48 and the return air @ 73, shouldn't the heat pump be able to run without using aux?
-
03-13-2008, 06:48 AM #8
If the stats aren't coming out of set back, then yea, there's a problem.
Are you using set back on the stats.
-
03-13-2008, 08:09 AM #9
Regular Guest
- Join Date
- Jan 2008
- Location
- Lehighton, Pa.
- Posts
- 171
On this system, the stats only control when the system goes on/off. All of the operations are controlled by the Harmmony board.
-
03-13-2008, 08:24 AM #10
Then there is a real good chance, the Harmony isn't set up right, or wired up right.