    Ohio
    MP580/581 TGP Question
    Why would anyone multiply both the set point and controlled variable input (separately) by 100, then bring them into a PID? This was for building static pressure control.
    You CAN choose the decimal places for both values.
    Is it an internal PID resolution issue?
    jogas
    Practically Canadian ehh.
    Decimal place limitations.
    Jan 2003
    I do it all the time. Decimal points are so much the problem with 32bit floats. I either have to use massive gains & integrals or just multiply the inputs and use normal P & I gains for good control.
    ie if set point is 0.02 and the input is 0.015 the PID needs some large gains, otherwise an error of 0.005 won't cause it to do anything. Now if the same PID sees 20 as the set point and the input is 15, error of 5, the gains can be "normal values" and I'll get a good control.
    Ohio
    Gentlemen, Thank you.
    jogas