    Quote Originally Posted by mayguy View Post
    The IAQ, you don't need to set it up at 2 stage cool to get the affect you are doing with the 802, as long the DHUM is wired to the board as the manual says.
    I am utilizing the control in a different method and do not require the IAQ to achieve. This can be achieved with any 2 stage control.

    Remove the BK jumper from the control board and wire Y1(Comfort Control) to Y(Furnace) to Y(Outdoor Unit)

    Wire Y2(Comfort Control) to BK(Furnace)

    Anytime Y1 energizes you will have 80% airflow. If Y1 satisfies the load conditions it will operate 80% for complete cycle. The only time you will have 100% airflow is when the comfort control energizes Y2.

    I do not utilize comfort-r (enhanced mode) with this configuration and would not recommend this setup if you are operating at low ambient conditions.

  2. #28
    Join Date
    Jan 2004
    Location
    PA
    Posts
    68,793
    That method may work.
    But you lose the ability the IAQ has to slow the blower during normal operation if the humidity rises while the unit is already running.

    For the cost difference between an IAQ and a 8321, you get more for the money with the IAQ. And no special wiring required.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  3. #29
    Join Date
    Dec 2002
    Location
    Rochester, MN
    Posts
    5,305
    HVAC.

    I did that set up with mine before I got my IAQ, did work out well, but like Been said, if the humidity is high, but the t-stat is running 2nd stage, you not going to get the dehumidity affect.

  4. #30
    Join Date
    Jan 2008
    Location
    Elkton, MD
    Posts
    141
    The IAQ thermostat has a single set of normally open dry dehumidification contacts that are designed to operate a whole house dehumidifier .

    In fact if you wire the dehumidification terminals directly to BK and the thermostat calls for dehumidification you would run 100% airflow in the cooling mode. You would be required to wire a seperate normally closed relay being controlled by the IAQ that would open on a call for dehumidification and remove the BK circuit to obtain 80% airflow.

    In the new ComfortLink/Acculink communicating models the new 900 series comfort control will continue to utilize the 3 degree overshoot method of dehumidification utilized by the 803 series control.

    While I realize that the method I utilize may not work for everyone, it has worked in every application I have attempted it in and it has reasonably controlled the humidity by increasing the run cycle and latent capacity of the system.

  5. #31
    Join Date
    Dec 2002
    Location
    Rochester, MN
    Posts
    5,305
    Quote Originally Posted by hvac-master View Post
    In fact if you wire the dehumidification terminals directly to BK and the thermostat calls for dehumidification you would run 100% airflow in the cooling mode. You would be required to wire a seperate normally closed relay being controlled by the IAQ that would open on a call for dehumidification and remove the BK circuit to obtain 80% airflow.
    No relay is needed. You wire BK right to the EIM.

    In the new ComfortLink/Acculink communicating models the new 900 series comfort control will continue to utilize the 3 degree overshoot method of dehumidification utilized by the 803 series control.
    The IAQ is able to overcool if the humidity is 5% over set point.

  6. #32
    Join Date
    Jan 2004
    Location
    PA
    Posts
    68,793
    DHM1/DHM2, are installer set up as to weather they are normally open or closed contacts.
    You set them up for the system you are installing. You can set them to open to slow the blower down. Or to close to slow the blower down.

    I think you misread the instructions.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  7. #33
    Join Date
    Jan 2008
    Location
    Elkton, MD
    Posts
    141
    I have reviewed the product data and stand corrected. It seems that this can be changed utilizing ISU 379.

    The problem is that this is not clearly explained in the installation instructions and is only identified in the product data manual.

  8. #34
    Join Date
    Dec 2002
    Location
    Rochester, MN
    Posts
    5,305
    Quote Originally Posted by hvac-master View Post
    I have reviewed the product data and stand corrected. It seems that this can be changed utilizing ISU 379.
    #379 to 1.

    Wire from R to DHUM 1 DHUM 2 to BK. No relay is needed.

    Then follow the jumper cutting on the notes.

  9. #35
    Join Date
    Jan 2004
    Location
    PA
    Posts
    68,793
    Once you use the IAQ, you will like the way it can control the blower.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  10. #36
    Join Date
    Jan 2008
    Posts
    91
    Quote Originally Posted by hvac-master View Post
    I am utilizing the control in a different method and do not require the IAQ to achieve. This can be achieved with any 2 stage control.

    Remove the BK jumper from the control board and wire Y1(Comfort Control) to Y(Furnace) to Y(Outdoor Unit)

    Wire Y2(Comfort Control) to BK(Furnace)

    Anytime Y1 energizes you will have 80% airflow. If Y1 satisfies the load conditions it will operate 80% for complete cycle. The only time you will have 100% airflow is when the comfort control energizes Y2.

    I do not utilize comfort-r (enhanced mode) with this configuration and would not recommend this setup if you are operating at low ambient conditions.
    Unknowing homeowner here... Does this mean BK controls fan speed in cooling mode only?

  11. #37
    Join Date
    Aug 2007
    Location
    Northern VA 38 degrees N by 76 degrees W
    Posts
    5,062
    Quote Originally Posted by Cub View Post
    Unknowing homeowner here... Does this mean BK controls fan speed in cooling mode only?
    Cooling and heat pump mode only, no fossil fuel

Page 3 of 3 FirstFirst 123

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event