Results 1 to 12 of 12
    50 amp circuit breaker heating
    I have a 42amp heat pump load on on both leads of a 50 amp double breaker, 240 vac. Lug connections are tight. After a year or so of no problems, this breaker has started to trip occasionally. The breaker heats up but not so hot that to touch is painful. Wires (awg 8, I think) do not appear to be heated.
    Is this normal for this load/breaker ratio?
    Any help will be appreciated.
    Irby
    Jul 2001
    Gold Coast of Connecticut
    I would call an electrician.
    Aire Serv of SW Connecticut- Gas heat, dual fuel and central a/c systems installed and serviced
    Northeast Ohio
    Circuit Breakers should not be operated above 80% of their rated load. Call the electrician.
    Southold, NY
    Solid or Stranded?
    Length of run?
    Actual incoming Voltage?
    These and several others ?’s need to be answered before an answer can be given.
    Breakers and wires should not be warm or hot.
    Bottom line Call an electrician
    http://www.powerstream.com/Wire_Size.htm
    Huntsville,AL
    wires in attic?
    in magnetic conduit?
    copper | aluminum?
    several trippings = new one!!!
    42 amps when you checked it.
    Could be spikes that are tripping it.
    42 amps is too much for a constant load on a 50 amp breaker.
    1- your breaker is oversized for the wire
    2-42A ought to be on a tad bigger breaker= bigger wire
    You gonna need an electrician
    Thanks for all of the quick replies. I'm going to check out all of the questions you asked and get back with the info.
    Irby
    Nov 2007
    Washington State (on the Peninsula)
    Call Electrician !
    Quote Originally Posted by irbyjr View Post
    Irby
    You need an electrician ASAP!
    That should have a 60 A breaker with 4awg thhn.
    Without knowing what you data plate calls for circut ampicity and using your 42 amps stated in your post ...
    42 x 125% = 52.5 you ned a 60 A breaker ...
    Now with a 60 A breaker you need 4 awg thhn.
    per NEC table 310.16 60 degree column.
    Jul 2000
    Northern Wisconsin
    Hopefully by now you've quit checking and have called a licensed electrician.
    50 amp breaker heating
    Thanks again for your advice and warnings. Actually, the circuit was deactivated before I posted the original question.
    Irby
    50 amp breaker heating up
    Seems as though this heat pump had an emergency resistance heater that supposedly had been disconnected long ago, but someone had re-connected it. The room thermostat was set too high on a cold morning and the backup heater did energize, apparently causing the high amperage that slowly heated the breaker. The unit is operating OK now with that backup heater circuit disconnected.
    Thanks for all of your comments.
    Irby