    Thumbs down 3m Warning

    Here's another one to watch for, homeowners & techs!

    3M Filtrete 16x25x4 media, to replace Honeywell F100 media

    Furnace suddenly cycling on limit. Tech read 192 at the limit. Found that the static pressure drop over the new filter was .55" WC. Taking filter out dropped temp at limit to 134. Static on the genuine Honeywell media was 1/2 that and the furnace didn't overheat.

  2. #2
    Join Date
    Jun 2004
    Location
    Howell, Michigan
    Posts
    16,158
    We had 3 service calls yesterday related to crappy filters. I did one, the husband offered my $20 to tell his wife it wasn't the filter......LOL

    I declined, told him he needed to buy something else though!
    Last edited by HeyBob; 02-27-2008 at 03:53 PM. Reason: can't spell

  3. #3
    Join Date
    Aug 2004
    Location
    North Richland Hills, Texas
    Posts
    14,914
    Home Depot changed from selling the Indiglo brand of 20x25x4 filters, which average about 50% more airflow resistance than the Honeywell media, to selling the 3M ones, which are even more restrictive.
    I have had service calls related to them, and expect to be pulling many more of them out of systems this spring during PMs.
    They say 20x25x4, but they are actually thicker than 4" to fit in the Honeywell and Air Bear filter housings.
    If more government is the answer, then it's a really stupid question.

  4. #4
    Join Date
    Aug 2004
    Location
    North Richland Hills, Texas
    Posts
    14,914
    Quote Originally Posted by HeyBob View Post
    We had 3 service calls yesterday related to crappy filters. I did one, the husband offered my $20 to tell his wife it wasn't the filter......LOL

    I declined, told him he needed to buy something else though!
    I have had similar experiences, but usually it is the wife asking me if I can say it was something other than her choice of filters that caused a problem.
    If more government is the answer, then it's a really stupid question.

  5. #5
    Join Date
    Aug 2002
    Location
    Office and warehouse in both Crystal River & New Port Richey ,FL
    Posts
    18,836
    3M may take the Oscar for killing more compressors than Paul Harvey did with electrostatic filters!

  6. #6
    Join Date
    Mar 2001
    Posts
    1,213
    Been tellen'em for years not to use the 'pleated' filters, too much restriction. Now going to be replacing furnaces because of them.

  7. #7
    Join Date
    Apr 2004
    Posts
    7,680
    Now in all fairness, the filter is a good filter but it's marketed as a direct replacement for an OEM filter which is where the problem is. If the contractor who designed the ductwork knew what he was up against, he would have built the duct system accordingly and ultimately sized the filter properly.

    It's not the filter's fault per sey, it's the schmuck who stuck it in the rack's fault and the "expert" at the store who said "This is the best filter for your money" when he didnt have any idea what he was talking about or what the application was.

  8. #8
    Join Date
    Apr 2001
    Location
    Camel City, NC
    Posts
    6,232

    wording

    I believe somewhere on the raper it says (some system efficiency may be sacrificed). This has been an ongoing problem and will continue.
    Be safe not fast. body parts don't grow back

  9. #9
    Join Date
    Feb 2007
    Posts
    999
    Quote Originally Posted by Moose View Post
    Been tellen'em for years not to use the 'pleated' filters, too much restriction. Now going to be replacing furnaces because of them.
    O.K., so as an average homeowner, I'm stuck behind a rock and a hard place. It's either the POS fiberglass jobs (now, they seem to be half a filter), or the MERV 8 pleated jobs.

    Been trying to find info on the web re: pressure drop, but it seems to be lacking.

    What would you recommend in a 1" filter?

    AM

  10. #10
    Join Date
    Jan 2008
    Location
    Lehighton, Pa.
    Posts
    178
    I agree with Ampulmans comments. Several weeks ago, everyone was beating the fiberglass filters stating that they let too much dirt through. Now were being told that these pleated filters are too restrictive. What gives?

  11. #11
    Join Date
    May 2007
    Location
    Naples, Fl
    Posts
    889
    Quote Originally Posted by ampulman View Post
    O.K., so as an average homeowner, I'm stuck behind a rock and a hard place. It's either the POS fiberglass jobs (now, they seem to be half a filter), or the MERV 8 pleated jobs.

    Been trying to find info on the web re: pressure drop, but it seems to be lacking.

    What would you recommend in a 1" filter?

    AM
    No more than 2 cfm per square inch to keep the velocity down so the filter has half a chance. Idealy .75 sq in per cfm.

  12. #12
    Join Date
    Jul 2000
    Location
    Northern Wisconsin
    Posts
    1,934
    A prime example of retail consumer products brought to market with the driving force being consumer demand instead of good solid research and concern for what harm the product will do. And the lawyers and bean counters going "No problem, we'll just purchase a large liability insurnace policy on the item and add that to the cost."

    Consumers beware....... if the filter that you're buying at the store isn't the same filter as the first one that the contractor installed when he put in your HVAC equipment you might be damaging your equipment or worse voiding the manufacturers warranty.

    If you feel the need to use extremely efficient air filters than realize that with few exceptions modifications will need to be made to your ductwork to maintain acceptable and safe air flow through the system. Just because it fits in the spot doesn't mean it belongs there.
    Use the biggest hammer you like, pounding a square peg into a round hole does not equal a proper fit.

  13. #13
    Join Date
    May 2007
    Location
    Naples, Fl
    Posts
    889
    Quote Originally Posted by jeepgrady View Post
    I agree with Ampulmans comments. Several weeks ago, everyone was beating the fiberglass filters stating that they let too much dirt through. Now were being told that these pleated filters are too restrictive. What gives?
    There is no contridiction here the system just can't be adversely effected by the better filter if it is then system performance takes priority over increased filtration.

Page 1 of 3 123 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event