    Hard-Start-Kits

    I am opening this thread as a follow up to another one opened yesterday. In that one, I explained that I was having an issue w/ lights flickering when my Heat Pump compressor turned on. Several pros suggested installing a Hard-Start-Kit (HSK) as a remedy. I decided to open a new thread to ask specifically about these kits. I am wondering what other pros think of this suggestion and if there is a particular Hard-Start-Kit manufacturer that is recommended.

    BTW, I intend to have the entire electrical system re-checked by a pro before installing the HSK. This includes having the electric company check the connections from the pole into the house, etc..

  2. #2
    Join Date
    Jun 2006
    Location
    SW MO.
    Posts
    5,212
    Here's what you are looking for.

    http://www.kickstartoem.com/faqs/homeowner.html
    Discipline your child so that other parents don't have to.

    We're awl pawthetic and kweepy and can't get giwrls. That's why we fight wobots.

  3. #3
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    68,117
    That, or the factory kit.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  4. #4
    Join Date
    Jun 2007
    Location
    Round Rock
    Posts
    3,561
    Chances are. A hard start kit really isn't going to do anything and not much can be done. It does work in rare occasions. Good luck.

  5. #5
    Join Date
    Mar 2004
    Location
    Grottoes VA
    Posts
    5,856
    I agree, I haven't had much luck with the hard starts curing the dimming lights problem.
    Karst means cave. So, I search for caves.

  6. #6
    Join Date
    Jul 2006
    Location
    Southern Ca, Elkton Md
    Posts
    7,572
    Have the electric company check the location of breaker.

    Is the breaker for the ac at the bottom of the panel?
    "Correct Installation is the Key"

    .1 has killed more HX then Rush Limbaugh

    What is your TESP?

  7. #7
    Join Date
    Feb 2008
    Location
    lugoff southcarolina
    Posts
    11
    I have used hard start kits to try and solve light flickering 90 percent of the time compressor is starting under a load most of the time i found txv not opening properly

  8. #8
    Join Date
    Jun 2006
    Location
    Southeastern Connecticut
    Posts
    841
    Quote Originally Posted by jeff bleckler View Post
    I have used hard start kits to try and solve light flickering 90 percent of the time compressor is starting under a load most of the time i found txv not opening properly
    What does that mean "Txv not opening properly" ?

  9. #9
    Join Date
    May 2006
    Location
    Amory Mississippi
    Posts
    1,002
    I used to work for a company that did thousands of new Ruud units in south Florida developments. In some areas they told me Ruud had them install hard start kits to eliminate the lights flickering when the condenser unit kicked on. This was because we had a call on the problem with a new carrier 410 unit and they wanted me to put a hard start on it. I checked all the connections back to the main and all the wire sizes were fine and voltages were fine. I was skeptical but installed the hard start kit and the problem went away. I just always felt if the maker of the equipment didn't feel the unit needed one I was not really fixing the problem with the hard start kit. They do work though.

  10. #10
    Join Date
    Feb 2008
    Location
    lugoff southcarolina
    Posts
    11
    what i mean by is txv is stuck shut or anouther term i call throteling

  11. #11
    Join Date
    Feb 2008
    Location
    lugoff southcarolina
    Posts
    11
    anouther thing i would check is mfd on capacitor

  12. #12
    Join Date
    Aug 2004
    Location
    North Richland Hills, Texas
    Posts
    14,914
    I have had very good success with using a quick start(just another term for a hard start) kit as a solution for the lights dimming problem. Sometimes there is still a slight flicker, but nothing near as severe as what it was before.
    Usually it is more noticeable when going from a unit with a recip compressor to a scroll compressor. The lock rotor amps are much higher on scroll compressors vs the same capacity recip.
    I have seen older houses with a 100-150 amp service that would brown out so bad that any digital clocks, VCR's, ect. in the place would loose their program. A quick start kit made it much better.

    The Kickstart brand, or an OEM kit is all I will install now.
    If more government is the answer, then it's a really stupid question.

  13. #13
    Join Date
    Sep 2007
    Location
    Shreveport, LA
    Posts
    64
    Quote Originally Posted by weber View Post
    Have the electric company check the location of breaker.

    Is the breaker for the ac at the bottom of the panel?
    Just curious weber. Should the breaker for the ac be located at the top?

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event