Air Temp
Been reading some of the posts re air temp at discharge vents. What is an acceptable temp range when both the heat pump and heat strips are running? The air discharging from my vents sometimes makes the vent too hot to touch for any length of time. Thanks.
-
02-26-2008, 09:00 PM #2
New Guest
- Join Date
- Feb 2008
- Posts
- 2
Air Temp out of a vent depends how close the vent is to your air handler. The further away you get the cooler you will find it. Not a big difference a few degrees. What you need to do is take a tempature rise on system. Go to the air handler and record temp in duct work near the air handler on both sides. you should get a temp difference of 45F to 55F. depends the size of unit and temp outside. Be asured that most furances have high limit protection. If it apears to be getting to hot and you feel safety is a issue call a professional for service.

-
02-26-2008, 09:11 PM #3
Actually, air temperature is a factor of Btu output and air volume. In most residential applications there should not be much, if any, difference between closer outlets and further outlets. If there is, there is something wrong with the insulation or there is air infiltration into the system.
Too hot of outlet air could be a sign of too little air. A dirty filter, indoor coil or any other obstruction to the airflow could be your problem. If it is not obvious, you should have an HVAC contractor diagnose your system for possible overheating factors that could cause major equipment failure.Government is a disease......masquerading as its own cureEcclesiastes 10:2 NIV
-
02-26-2008, 09:17 PM #4
Regular Guest
- Join Date
- Feb 2008
- Location
- lugoff southcarolina
- Posts
- 11
air temp coming out will vary depending how kw stripes are and what your outside temp is;

-
02-26-2008, 09:23 PM #5
Regular Guest
- Join Date
- Jun 2007
- Location
- The Twilight Zone
- Posts
- 2,964
Assuming you have proper air flow, a heat pump will put out 90 degree air at 32F outside temperature. If you have 15kw electric strips energized along with the heat pump, you'll get about another 34 degrees, for a total of 124 degrees roughly. Your hand is about 91 degrees, so this will feel very hot to the palm of your hand.
Take care.
-
02-26-2008, 09:26 PM #6
Waiting Email Confirmation
- Join Date
- Feb 2004
- Location
- Ohio
- Posts
- 276
How long is the unit running during this process? Most stats stage the electric heat on should not all come on at once, if is thats not right. With heat pump running should only be a bank of heat coming on not all of them.
-
02-26-2008, 11:30 PM #7
Regular Guest
- Join Date
- Nov 2007
- Location
- Livermore, Ca
- Posts
- 163
This HO gets 120* at the farthest register when both are running.
-
02-27-2008, 05:52 AM #8
-
02-27-2008, 07:23 AM #9
Regular Guest
- Join Date
- Jun 2007
- Location
- The Twilight Zone
- Posts
- 2,964
-
02-27-2008, 07:30 AM #10
Around here, 2.5 and some 4 ton units have 15 KW.
Makes a big difference on discharge temp
-