    What size is it.
    What size wire is it.
    What is the length of the feed.
    Is teh breaker for the OD unit, at or near the top of the panel box.
    2ton Scroll (don't know the amps)
    #10 copper
    about 38 ft.
    60 amp non-fused disconnect
    2nd breaker down
    Good constant voltage at panel
    HP, or AC.
    TXV or fix metering, for ID and OD.
    Nov 2000
    Eastern PA
    On a loaded panel box, when the A/C, breaker is on the bottom. The bus drops voltage, and can flicker lights sometimes.
    Yep. Just wanted to second this because it is sometimes an easy way to get rid of an annoyance that also wears on light bulbs (low voltage = high amperage = lower bulb life).
    ...seek, and ye shall find;..
    Ecclesiastes 10:2 NIV
    One leg of your 240v main panel could have more inductive loads, like fridges or any unit that has an AC motor in it, causing a load imbalance. A open neutral could also cause light flickering but can be difficult to find.
    Phoenix AZ
    try using a kick start for the commpresser it sometimes helps
    Feb 2007
    Las Vegas,NV
    I dont see as many problems with alot of the newer houses that have underground service, but some of the older houses that have overhead power service tend to develop problems over the years, especially in windy areas. Years and weather can take its toll on connections. I have found people in the past complain about bulbs burning out to frequently and found that most of the time the cause was a loose neutral in the circuit box. I installed a tempstar rtu on an old 60s house back in 02, a couple years later the homeowner called me complaining that on a hot day after the unit shut down, it would not restart without straining itself and sometimes tripping the breaker. This was a scroll compressor. last summer, they were on the back porch one night and when the unit restarted, they saw showers of sparks coming down from the power pole out back. Turns out they had a severly loose connection up by the transformer. After that, they never had another problem with the unit trying to restart or trip the breaker. Make sure all your connections are secure, and if you have an older overhead service, it wouldnt hurt to have that checked out once in a while also.
    Jul 2002
    Slacking off right now
    Electrican told me - it depends upon how far you are from the pole transformer as well
    www.vetopropac.com - The best tool bags on the market - The offical tool bag of choice by techs everywhere
    Arguing with some people is like wrestling a pig - eventually you realise the pig actually enjoys it
    Gonads serve a useful purpose but are no substitute for brains
    Apr 2003
    California
    Thumbs down
    you have a ducane - be glad it does anything, has your TXV failed yet?
    Quote Originally Posted by dave82323 View Post
    No.