    Thanks everyone for the input. I knew it just didn't sound right. I don't think he is trying to scam me but rather he really believes it would work. He had been in the industry for years and is now semi-retired. I'm sure he was thinking he was doing me a favor and saving me big $$$. I'll look into replacing the whole unit by a licensed contactor that will ensure my peace of mind.

  2. #15
    Join Date
    Apr 2007
    Posts
    6,285
    edit......
    Last edited by BigJon3475; 02-26-2008 at 10:47 PM.

  3. #16
    Join Date
    Aug 2002
    Location
    Office and warehouse in both Crystal River & New Port Richey ,FL
    Posts
    18,836
    Quote Originally Posted by cap2240 View Post
    I have a 12 year old split system 5-ton Lennox AC, gas furnace in a 2000 Sq foot home that heats fine but needs a new cooler.

    I was going to replace everything until a friend of a friend who does AC work suggested I install a new Goodman 13 SEER R22 unit outside and keep the Lennox coils from my existing 10 SEER unit. He said he checked with Lennox and that the coils will work with the new unit.

    I'm new to all this but read you need to match the coils to the new system to achieve the stated SEER rating. Is this correct?

    Any thoughts would be greatly appreciated?
    If and only if both pieces were the same brand and an approved match,then maybe,still likey better off wih both being matched and new.

  4. #17
    Join Date
    Nov 2000
    Location
    Eastern PA
    Posts
    68,852
    Quote Originally Posted by dash View Post
    If and only if both pieces were the same brand and an approved match,then maybe,still likey better off wih both being matched and new.
    See now, we can completely agree on some things.
    Government is a disease...
    ...masquerading as its own cure…
    Ecclesiastes 10:2 NIV


  5. #18
    Join Date
    Aug 2002
    Location
    Office and warehouse in both Crystal River & New Port Richey ,FL
    Posts
    18,836
    Quote Originally Posted by RoBoTeq View Post
    See now, we can completely agree on some things.
    Maybe this,not much else.

  6. #19
    Join Date
    Aug 2003
    Posts
    466
    Quote Originally Posted by dash View Post
    Maybe this,not much else.
    Just curious, are you normally a disagreable sort of person?

  7. #20
    Join Date
    Aug 2002
    Location
    Office and warehouse in both Crystal River & New Port Richey ,FL
    Posts
    18,836
    Quote Originally Posted by everythingair View Post
    Just curious, are you normally a disagreable sort of person?
    No ,not at all.

  8. #21
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    66,755
    Quote Originally Posted by everythingair View Post
    Just curious, are you normally a disagreable sort of person?
    ROFL
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  9. #22
    Join Date
    Aug 2002
    Location
    Office and warehouse in both Crystal River & New Port Richey ,FL
    Posts
    18,836
    Quote Originally Posted by beenthere View Post
    ROFL
    Just so you know beenthere,your ROFL ,




























    made me laugh!!

Page 2 of 2 FirstFirst 12

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event