    Repititive time delay failures

    I installed a 13 Seer Rheem Achiever package unit. A call back found a froze up coil due to a faulty fan delay on off-relay - 4 weeks old. ( The indoor blower pulls in immediately and then runs 50 seconds longer than compressor when T/stat is satisfied.) 2nd one failed today - at 8 weeks. My open circuit voltages are 249 VAC and 29 VAC for the control circuit. Everything else looks good. I'm down by the Everglades and we have plenty of storms now so I always put in a Supco surge protector with each unit. Now surges may still be an issue - but can excessive voltage kill these little stinkers?

  2. #2
    Join Date
    Mar 2013
    Location
    East Concord, NY
    Posts
    22,646
    Post Likes
    i dont consider 249 excessive voltage. 269, 299 yeah, but not 249 or even 29. i see that everyday. what is the closed circuit voltage? high amps will kill anything that is not rated for it.
    Nest is POO!!

  3. #3
    Join Date
    Jun 2006
    Posts
    18
    Post Likes
    Thread Starter
    The incoming voltage drops to 245 VAC - the control voltage drops to 27 VAC when unit is running.

  4. #4
    Join Date
    Mar 2013
    Location
    East Concord, NY
    Posts
    22,646
    Post Likes
    no problems there. maybe a a voltage fluctuation or a fan stopping/motor overheating when you are not there?
    Nest is POO!!

  5. #5
    Join Date
    Jun 2004
    Location
    St Paul, minnesota
    Posts
    1,527
    Post Likes
    eliminate the time delay!

  6. #6
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    Quote Originally Posted by ripley,fla View Post
    I installed a 13 Seer Rheem Achiever package unit. A call back found a froze up coil due to a faulty fan delay on off-relay - 4 weeks old. ( The indoor blower pulls in immediately and then runs 50 seconds longer than compressor when T/stat is satisfied.) 2nd one failed today - at 8 weeks. My open circuit voltages are 249 VAC and 29 VAC for the control circuit. Everything else looks good. I'm down by the Everglades and we have plenty of storms now so I always put in a Supco surge protector with each unit. Now surges may still be an issue - but can excessive voltage kill these little stinkers?
    What is the voltage rating given on the equipment label? If this is single phase, why is the voltage so high?

    I would use an ICM monitor to make certain that there is a countdown to activation after a power problem, and a lockout if there is a problem.

    You can get extended fan run time by using a stat such as a Vision Pro, and configure for extended fan run time in installer setup.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  7. #7
    Join Date
    Jun 2006
    Posts
    18
    Post Likes
    Thread Starter
    The unit calls for 230 VAC - it is a single phase unit. The voltage is what it is - the mobile home park is about a half mile from a sub station - but it shouldn't be a reason for 250 VAC supply. The monitor may be an option - the vision pro may allow me to 's**tcan the time delay. And just throwing away the time delay is also an option! Thanks for all answers. I'll see if my Rheem dealer can hook me up with a factory guru. Usually I hear "we have never had that problem before"

  8. #8
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    You should contact the power Co.

    The final voltage you get at the park is from the last transformer, and it may be defective or need a different turns ratio to be able to supply the correct voltage.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  9. #9
    Join Date
    Feb 2009
    Location
    Manchester, TN
    Posts
    399
    Post Likes
    Don't the rheem 13 seers use the x-13 motors? Those modules can do some weird intermittent things. the 249 volts won't be an issue. That is within the units specs. Now if you get over 252 volts you could start seeing issues. Oddly enough the power company in my area can legally send 256 volts.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •