    How would I find out what the SEER rating in my old heat pump is?
    I have a 2.5 ton York heat pump. Approx 14 years old. Model # B3PS030A06A, serial # NKAM151183 It's been falling apart during the past year. The compressor still works great, but everything else is failing due to age. Leaks, Accumulator rusted through, control board, etc.
    I'm having it replaced with a larger 3 ton Rheem RQPL series 14 SEER with 410A refrigerant.
    I would like to know the SEER rating of the old unit and how much (ballpark) can I expect to save with the new one? 10%, 40% How much?
    Jun 2007
    The Twilight Zone
    When I replaced my 21 year-old 7 SEER Trane heat pump with a new 14 SEER, 12 EER Goodman, I saw a 40% reduction in kilowatt consumption comparing Aug '07 with August '06. These months were similar in average temperature for my area. To do a more accurate analysis would require the #of cooling degree days.
    I would ballpark 30% savings for your upgrade from a 14 year old unit. A little more if that old unit was low on refrigerant.
    Good luck.
    SC
    Someone else might be able to give you an exact SEER rating for your old equipment.
    But I would like to point out that the SEER rating was given for NEW equipment. You said yourself that yours is falling apart and has leaks. The actual SEER is probably half the original SEER, based on your comments. But it's only a guess at this point. The only way to get an accurate number at this point would be to have your old system SEER tested. You can bet the new system will run cheaper than the old one you describe.
    Massachusetts
    Quote Originally Posted by gary_g View Post
    This really isn't true. If you take the actual SEER of the system (not the manufacturers NAME of the system and subtract the old SEER number, divide that by the new SEER number, you should get the per cent of savings. For example, if your new system is truly 14-SEER, coming from a 7-SEER, you should see a 50% savings. Since you only saw 40%, it's safe to assume that either your old Trane unit was delivering more than 7-SEER or more likely, the new system is only doing about 12-SEER. You see, the SEER rating is actuallly the number of BTU's of work you'll get for each 1-watt of electricity used. So if you actually got 14 Btu's per watt with the new system and 7 Btu's per watt from the old, then clearly the new system would twice as efficient or use 1/2 the electricity for a 50% savings. Since you only saw a 40% savings, a 40% improvement over 7-SEER would be 12-SEER. See?
    I don't know
    SEER is not necessarily an accurate indicator of efficiency; it's a lab test figure used to compare equipment.
    Quote Originally Posted by amd View Post
    Considering that all efficiency (SEER, EER, COP, HSPF ) ratings are lab test.
    No one gets the rating.
    Jun 2007
    The Twilight Zone
    Quote Originally Posted by skippedover View Post
    Hello.
    That is very incorrect.
    True cooling costs are determined by EER and not SEER. SEER is not "actuallly the number of BTU's of work you'll get for each 1-watt of electricity used". That is the definition of the Energy Efficiency Ratio (EER) = system cooling btus / divided by the condenser power draw in watts (at 95F laboratory conditions). A 36,000 btu system that draws 3000 watts is 12 EER.
    For a fixed speed fan in the air handler:
    SEER = EER (at 82F) x fudge factor. The fudge factor is the Cyclic Degradation Coefficient.
    For a variable speed fan in the air handler, the SEER calc is much more complicated and involves calculating the EER at 10 bin temperatures ranging from 67F to 102F in 5 degree increments. The lowest 3 temps make up 66% of the value of the calc while the highest 3 temps account for only 7% of the calc.
    SEER is a bullsh%t number geared towards lower operating temps. Just because a system is high SEER, doesn't mean it is cheaper to run. Some 16 SEER systems do not achieve a 12 EER. A high EER system is always cheaper to operate than a lower EER system.
    Info from ARI Standard 210/240, Performance Rating of Unitary Air Conditioning and Air Source Heat Pump Equipment.
    Page 82 for fixed speed air handler.
    Pages 82 - 86 for variable speed air handler.
    Take care.
    Quote Originally Posted by Dave_C View Post
    Hello All,
    1993---- 28,200 btu--------10 seer