    Quote Originally Posted by weber View Post
    I see it more often then you would think!

    I have calculated 90% running at 67%, with no problems other then gas consumption. Thats what a combustion analyzer is for. And the customer loves you next month when they get thier bill!

    But yeah, for this scenarios we are assuming that everything is operating properly.

    I think its understood what you were implying here.

  2. #28
    Join Date
    Feb 2008
    Posts
    1,275
    Quote Originally Posted by weber View Post
    I see it more often then you would think!

    I have calculated 90% running at 67%, with no problems other then gas consumption. Thats what a combustion analyzer is for. And the customer loves you next month when they get thier bill!

    But yeah, for this scenarios we are assuming that everything is operating properly.
    A derated furnace can still have efficient combustion. The furnace could still be technically utilizing 90% of the fuel for heating the space. I think in the case of a derated furnace, gas pressure readings and a meter test would be more useful tools to employ.

  3. #29
    Join Date
    Jan 2004
    Location
    PA
    Posts
    68,770
    Quote Originally Posted by Frostie View Post
    I think in the case of a derated furnace, gas pressure readings and a meter test would be more useful tools to employ.
    You still wouldn't know the efficiency it was at. All you would know is the input rate. You wouldn't know how high the excess air was. So you wouldn't know how much you were cooling the flame.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  4. #30
    Join Date
    Dec 2007
    Location
    Ohio
    Posts
    2,876
    Quote Originally Posted by Frostie View Post
    A derated furnace can still have efficient combustion. The furnace could still be technically utilizing 90% of the fuel for heating the space. I think in the case of a derated furnace, gas pressure readings and a meter test would be more useful tools to employ.
    You're right that it can still have somewhat efficient combustion....however how would you know that if you weren't using a combustion analyzer??? Most furnaces will tell you to set the gas pressure at 3.5 IWC ... assuming that it is either a single stage or in high fire ... however, I have rarely seen then left at 3.5 when they are set up properly with an analyzer. Pressure readings can get you kinda close....but never truly dialed in.
    I need a new signature.....

  5. #31
    Join Date
    Jan 2008
    Posts
    2,118
    Back to the original post - I think the OP answered his own question. Throw away 20 cents on each dollar of gas, or 10 cents on each dollar of gas. Which is more efficient?
    Get a 90%(or better) furnace, with variable speed blower, properly installed, and forget about the 80% piece of junk.

Page 3 of 3 FirstFirst 123

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event