    We have a new customer with 3 two-story buildings (all set up identical) in the same complex. The buildings are from the 80's (and running dual pressure pneumatics ) but the roof top units were replaced about 4 years ago. Each floor has one 60 ton Carrier gas pack (2 units per building). The units are controlled by a CCN to Ethernet converter box. There is one box per building to control the 2 RTUs. I am able to connect via a dial-up connection to each converter. I have a couple of questions on this set up.
    Can the converter act as stand-alone controller? (The units have ComfortLink controls) or should there be a controller somewhere in the complex? I looked everywhere for a CCN controller but could not find one. The only connections on the converters are a phone line, the COM1 and ofcourse power.
    I tried to direct connect to the controller using a null modem cable but nothing happens. I made my cable connections and hit "enter" like the manual said but nothing happens.
    Melbourne,Aus
    Quote Originally Posted by acbandit_328 View Post
    The ethernet converter only converts CCN protocol from RS485 to run over ethernet, it is not a controller. It sounds like if the converter only has a phone line connector, com1 and power it is a Telink dialup module!! Can you get model numbers from the items you are talking about so more investigations can be done??
    Aus..
    Las Vegas, NV
    Yes. I'll get model #s today. What all do I need? RTU model #?
    Melbourne,Aus
    No I dont require the RTU model #s only the CCN boxes.
    Las Vegas, NV
    that's the thing....I can't find any other CCN boxes. It looks like the CCN-to-ethernet converter is connected directly to the ComfortLink controls on the RTU. Should I have a controller somewhere? or can the CNN-to-ethernet converter be used just to look at the ComfortLink controls on the RTU via a dial-up connection?
    Melbourne,Aus
    If you are able to connect to the system via dialup I assume that you are doing this using Comfortview or Servicetool software!! if this is the case then it is most likely a Telink modem connected to both units on each building. Info on both the Telink & ethernet converter are attached:-
    Las Vegas, NV
    Aus...when I click on your pdf attachments, I only get a blank page. Do you know the website where I can download the attachments from?
    Also....when I dial into the systems, I use a network connection on my computer and then I use my web browser to connect. When I connect, I get the Carrier CCNWeb page and I can see the 2 RTUs. Does this mean I should have a CCNWeb controller somewhere?
    Melbourne,Aus
    Yep, if you get the CCNWeb screen up you definately got a CCNWeb somewhere. Put your email in your profile and I will email you the docs.
    Aus..
    Las Vegas, NV
    Aus, I think you are right. I think Telink. Here are the numbers on the back of the box: 3504N029807 00-02-52-00-0E-9C. Thanks!
    Las Vegas, NV
    my e-mail address in now on my profile.