on my tstat i have emr set to on and it doesnt show it raise the temp in 1 degree increments and it seems to go on high fire when I just tested it
I set a 7 degree rise setpoint for 40 minutes from now
then I turned E off and raised it 5 degrees and it sounded the same to me
-
02-26-2008, 04:42 AM #42
Professional Member
- Join Date
- Feb 2007
- Location
- 18951
- Posts
- 1,593
-
02-28-2008, 07:15 AM #43
Are you still asking about a mod thermostat or a heat pump thermostat?
If it's a mod thermostat in a dual fuel system, then depending on the "aux off" set point you have programmed and the outdoor temp. If your aux off set point is 35 and your OD temp is 40, then no, the aux heat (fossil fuel) will not come on. If it were set to 40 and it was 35 OD, then yes, if the recovery feature were turned off, it would kick the system into high fire because you programmed it to do just that.