How many watts does my heat pump use?
I couldn't find this information on the unit or online. It is a Trane 3 Ton split heat pump, outdoor section model # 4TWX4036A1000AB, Indoor section model# 4TEE3F37A1000AA.
I would like to know how many watts are used with just the heat pump running and with heat pump and emergency heat.
Thanks for the help.
-
02-15-2008, 01:25 PM #2
Professional Member
- Join Date
- Sep 2005
- Location
- Texas
- Posts
- 2,793
volts X amps = watts
-
02-15-2008, 01:29 PM #3
The watts the HP uses will vary as the OD temp varies.
The colder it is, the less watts it uses, it also provides less heat.
You need to know the KW rating of your aux heat to know how many watts it uses.
-
02-15-2008, 01:33 PM #4
Regular Guest
- Join Date
- Feb 2008
- Location
- NC
- Posts
- 15
-
02-15-2008, 01:40 PM #5
The same size air handler can have different size strip heater packages.
Contact the installing contractor, he should have the spec guide for the unit.
-
02-15-2008, 01:51 PM #6
The heat strip size should be marked on the exterior of the Air Handler.
It is located on the data plate with model/serial. Below model/serial are several boxes and 1 should be checked or filled in to indicate what size heater is in the unit. Some people write in on the outside of the cabinet with marker to make it easier on the techs that come out.
then, like said before, volt x amps = watts.
example.... 10KW heater rated at 60 amps at 240 volts....
60 x 240 = 14,400 watts.
That is not exact nor will it be with your unit. Because the amps won't be exactly 60 and the voltage won't be exactly 240. Have a service tech take the measurements for you at your next routine service. Then you can do the math on your time.
-
02-15-2008, 01:59 PM #7
Professional Member
- Join Date
- Apr 2005
- Location
- NE PA
- Posts
- 697
-
02-15-2008, 02:17 PM #8
Regular Guest
- Join Date
- Jun 2007
- Location
- The Twilight Zone
- Posts
- 2,964
That is a 3 ton heat pump.
I can give you figures for my 3-ton Goodman heat pump so they should be in the ball park. The kw's are for the outside unit only.
60F, 2.86 kw
50F, 2.75 kw
40F, 2.64 kw
30F, 2.6 kw
20F, 2.53 kw
10F, 2.41 kw
0F, 2.30 kw
-10F, 2.19 kw
Hope this helps.
Take care.
-
02-15-2008, 02:56 PM #9
Professional Member
- Join Date
- Feb 2007
- Location
- 18951
- Posts
- 1,593
The easiest and most accurate way to find out is to turn everything off except the heat pump system and check your electric meter. First with no electric backup, and then with it.
-
02-15-2008, 03:33 PM #10
Professional Member*
- Join Date
- Nov 2004
- Location
- SW FL
- Posts
- 5,251
Designer Dan
It's Not Rocket Science, But It is SCIENCE with "Some Art".

Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities
-
02-15-2008, 04:05 PM #11
14 SEER = 14,000 btu/ kwh
36,000btu = 2.57kw
-