Page 1 of 4 1234 LastLast
Results 1 to 13 of 45
    NC
    How many watts does my heat pump use?
    I couldn't find this information on the unit or online. It is a Trane 3 Ton split heat pump, outdoor section model # 4TWX4036A1000AB, Indoor section model# 4TEE3F37A1000AA.
    I would like to know how many watts are used with just the heat pump running and with heat pump and emergency heat.
    Thanks for the help.
    volts X amps = watts
    Lancaster PA
    The watts the HP uses will vary as the OD temp varies.
    The colder it is, the less watts it uses, it also provides less heat.
    You need to know the KW rating of your aux heat to know how many watts it uses.
    NC
    Where can I find the rating for my aux heat? Is is not the same for all of the model # I listed?
    Is the a graph somewhere of the HP power usage?
    Lancaster PA
    The same size air handler can have different size strip heater packages.
    Contact the installing contractor, he should have the spec guide for the unit.
    Western NC
    The heat strip size should be marked on the exterior of the Air Handler.
    It is located on the data plate with model/serial. Below model/serial are several boxes and 1 should be checked or filled in to indicate what size heater is in the unit. Some people write in on the outside of the cabinet with marker to make it easier on the techs that come out.
    then, like said before, volt x amps = watts.
    example.... 10KW heater rated at 60 amps at 240 volts....
    60 x 240 = 14,400 watts.
    That is not exact nor will it be with your unit. Because the amps won't be exactly 60 and the voltage won't be exactly 240. Have a service tech take the measurements for you at your next routine service. Then you can do the math on your time.
    Apr 2005
    NE PA
    Quote Originally Posted by air2spare View Post
    Actually volts x amps = VA
    volts x amps x PF = watts
    Compressors are not unity PF so there is some difference (watts will be lower than VA by 10-15&#37.
    paul
    Jun 2007
    The Twilight Zone
    Quote Originally Posted by adama View Post
    That is a 3 ton heat pump.
    I can give you figures for my 3-ton Goodman heat pump so they should be in the ball park. The kw's are for the outside unit only.
    60F, 2.86 kw
    50F, 2.75 kw
    40F, 2.64 kw
    30F, 2.6 kw
    20F, 2.53 kw
    10F, 2.41 kw
    0F, 2.30 kw
    -10F, 2.19 kw
    Hope this helps.
    Take care.
    Feb 2007
    The easiest and most accurate way to find out is to turn everything off except the heat pump system and check your electric meter. First with no electric backup, and then with it.
    SW FL
    2.85 kW average for 4TWX4036
    8 kW or 10 kW may be typical auxiliary heat on a 3-ton for Southern U.S. 10 to 15 kW for Northern U.S.
    Designer Dan
    It's Not Rocket Science, But It is SCIENCE with "Some Art".
    Morehead City, North Carolina
    14 SEER = 14,000 btu/ kwh
    36,000btu = 2.57kw
    Jun 2007
    The Twilight Zone
    Quote Originally Posted by capecool View Post
    Wrong (sorry). So a 14 SEER only produces 14,000 btu/hour? That would be a little more than 1 ton.
    SEER = EER (at 82F) x fudge factor, for a fixed speed air handler.
    For a v-s air handler, the calc is much more complicated.
    Take care.
    Jun 2007
    Metro St. Louis
    Quote Originally Posted by gary_g View Post
    Gary - I think you misread what he said. It was per kilowatt hour.