    quick question about blower

    I had a tech at my house recently and he adjusted the blower speed on my unit due to low "delta T" .

    I now notice that the furnace kicks on and runs no problems. Then the thermostat reaches the set point and clicks to turn the furnace off and the blower cycles up to a higher speed for about 90 seconds.

    I didn't notice it before the blower speed was adjusted.
    Is this normal? (goodman 93% eff furance downflow)

  2. #2
    Join Date
    Mar 2004
    Location
    Grottoes VA
    Posts
    5,849
    Post Likes
    call them back, they wired it wrong
    Karst means cave. So, I search for caves.

  3. #3
    Join Date
    Feb 2008
    Location
    Florida
    Posts
    146
    Post Likes
    Its probably a variable speed motor and the tech set the dip switces for a 90 sec blower off delay if goodman offers this. If its a gas furn its probably 120volts, and if the heat woks I doubt its wired wrong.

  4. #4
    Join Date
    Jun 2000
    Location
    WYO
    Posts
    2,187
    Post Likes
    Model # ?

  5. #5
    Join Date
    Feb 2007
    Posts
    106
    Post Likes
    Thread Starter
    model is gch90703bx

  6. #6
    Join Date
    Jan 2008
    Location
    In the work truck
    Posts
    3,275
    Post Likes
    from what i have noticed on goodman systems this is normal. the speed for the blower off delay as well as the "fan on" are the same. the system uses the cooling fan speed for these 2 functions. However, i have a question. are all of your supply and returns open all the way including the dampers? I would ask your service company. was this a new install? How did they size the system? do they know the ductwork has enough air flow for the amount of cfm?

  7. #7
    Join Date
    Feb 2007
    Posts
    106
    Post Likes
    Thread Starter
    all supplies and returns are open all the way. not a new install they just came out to install a condensate pump and configure the blower speed.

    the rest I don't know as it wasn't a new install.

  8. #8
    Join Date
    Feb 2007
    Posts
    106
    Post Likes
    Thread Starter
    any thoughts? it just seems strange to me but maybe its just strange because its different now

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •