+ Reply to Thread
Results 1 to 18 of 18
Thread: weird failures with grasslin clocks
    Aug 2013
    Omaha
    I've come across 3 clocks that all failed in the same way...2 of them were a littler older, 1 was under 4 months old.
    Just wondering if anyone else has came across grasslin clocks that don't terminate..??
    All 3 of these calls within a month of each other, customers complained of excessive condensation on the ceiling and dripping/freezing on the floor. So I'm first suspecting the obvious that its staying in defrost too long.
    And sure enough it was the clocks all 3 times....checked across N and X @ evaps and had 0 volts so 3 wire working ok...went to timer and everytime found voltage at X terminal but timer not terminating.
    Now, the ones I replaced weren't the newer DTAV40 they were something like DTSX-240-M or along those lines.
    I've read on here recently that all these weird issues have been fixed with the DTAV40..?
    My boss still doesn't like them and advises us to replace with a paragon when its not a warranty issue
    Nov 2007
    Tucson, AZ
    Replace those POS with a Paragon and be done with them. The fail within a year. I am not impressed with Grasslin
    Quote Originally Posted by N2fords View Post
    No patience or tolerance for Grasslin clocks.
    Aug 2013
    Omaha
    right....thanks guys.
    The only thing i do like that grasslins have that paragons don't is each defrost can be set for different lengths..
    But isn't there a paragon that can do that too?
    Nov 2007
    Tucson, AZ
    You are mistaken as paragon digital have desperate duration and if the power goes out it will keep the time.. best time clock out there..
    Dec 2006
    In a Mess
    +1 i love those
    Sig removed by mod. G-Rated site
    Nov 2007
    Tucson, AZ
    All I use period
    Mar 2014
    I just tell customer to use hair dryer works every time. Just kidding
    Paragon electromechanical clocks are great! They can do any type of defrost
    Jan 2014
    Idaho
    9145-00 the only time clock you need
    Aug 2013
    Omaha
    Is the 9145 dual voltage?...or do I need a 9145-20 as well?
    Jul 2000
    Guayaquil, EC
    Quote Originally Posted by UmmScott View Post
    It automatically selects for dual voltage.
    http://www.uni-line.com/images/docs/150-1893d.pdf
    Sep 2012
    northern Ohio
    Quote Originally Posted by Idahoreferman View Post
    Used to have a whole shelf in the van for defrost timers, now I have two. both 9145-00, always carry a back-up.
    Jan 2014
    Idaho
    Quote Originally Posted by refrigeration johnny View Post
    Yep the only way to roll
  14. #14
    Aug 2013
    Omaha
    damn....so why have I been clowning around this whole time and just stocking this one? haha
  15. #15
    Aug 2014
    Fuquay-varina, N.C.
    I love Grasslin.......when I am throwing it off the roof!
    Right after I look at the new Paragon I just installed!! Golden!
  16. #16
    May 2014
    Bay Area California
    Here's one for you. Service call earlier this week. Evap frozen up pretty good. Pins not set to ever defrost. See if you guys come to the same conclusion I did . . .
  17. #17
    Apr 2013
    SE Nebraska
    One time a grasslin caught on fire on top of the freezer box. It was a 2 alarm fire, the only damage was to some wires to freezer and the POS that caused/deserved the flames.
  18. #18
    Aug 2014
    Fuquay-varina, N.C.
    Had a nice one today! Walk in freezer. Contractor installed time clock 6" to the left of the evap on the wall! Anyhow, it works! But the call today was the freezer was warming up. Upon arrival I found boxes on top shelf jammed up against the timer...........ok! Cleared the boxes, ran a defrost.
    ( the evap was Really frosted up!) defrosted great. Hoping without the boxes holding the timer back, tonight will be quiet.
+ Reply to Thread