I Came In On This In The Middle And Im Not And Engineer But It Would Seem To Me That Your Electric Heat Is The Source Of Yur Problem. Your Electric Problems Occured When You Started Using 2nd Stage And Aux. You Have 20 Kw Of Electric Heat Which Seems High To Me But Im Not Sure About Your Climate. Your Heating Stages Are All Tied Together As Per The Picture You Submitted. When Ive Done It Before, W1 And W2 Are Wired Through Seperate Outside Stats And Your Output From Your Condenser During Defrost Should Be Connected To W3. Assumming That The Charge Was Properly Weighed In, The Pipe Sizes Are Correct And The Pressures Match The Chart In The Service Facts,the Filters Are Clean Etc, Your Problem Sounds To Be Electric Heat Related. My Old Boss Used To Say "dont Chase Btu's Down Rat Holes" Youll Find That Most Problems Are Very Simple And Have A Way Of Getting Complicated
-
02-15-2008, 08:52 PM #54
Regular Guest
- Join Date
- Jan 2008
- Posts
- 7
-
02-15-2008, 10:48 PM #55
Regular Guest
- Join Date
- Mar 2007
- Posts
- 55
Because of the crappy weather we've been having lately here in Ohio, the installers finally were able to come out today to check things out. One thing that was discovered was that the wire going to one set of heat banks was loose so I was only using the set of banks when aux was on. I know that made a big difference in the temperature output at the register is it shot the temperature up from 100 to 126. If I was only using 1 heat bank and the electric bill was so high, I have to wonder if fixing this could make the electric usage worse...
They also did some tweaking to the heat pump to get it more inline with factory specs. Before the tweaks, they were showing the BTU output at just over 20,300 (at 32 degrees) and after they tweaked it, the BTU output was 23,200. With the tweaks it raised the COP number to just above 3 and the EER was raised to be 10.2.
Aside from those 2 changes, they said everything else was in order and correct, including how the dip switches were set. They said the airflow setting (even though it appears to be set to 3.5 tons) is set correctly since they're getting about 1200 cfm. And they said that they always set the aux airflow setting to be lower as it helps to increase comfort.
In a couple of days, we're supposed to have some pretty cold days again so I'll be able to tell if the changes that were made had any effect whatsoever on the electric usage. Once I am able to determine that, I'll let everyone know my findings.
-
02-16-2008, 06:28 PM #56
All of this info for a residential topic? Pro Forum , you think?
-
02-17-2008, 08:37 PM #57
Professional Member*
- Join Date
- Aug 2007
- Location
- Northern VA 38 degrees N by 76 degrees W
- Posts
- 3,251
-
02-17-2008, 09:04 PM #58
Regular Guest
- Join Date
- Mar 2007
- Posts
- 55
I know when they left, they told me that if I wanted them to, at any time they would call a Trane specialist to come down to take a look at things. Is it normal for the heat pump to need "tweaked" to get it optimized? How is it possible to have better numbers out in the field than the factory?
-
02-21-2008, 10:01 PM #59
Regular Guest
- Join Date
- Jan 2008
- Posts
- 7
I DONT WANT TO PASS JUDGEMENT ON YOUR CONTRACTOR. IF YOU THINK HE DESERVES THE BENEFIT OF THE DOUBT, CONSIDER THE ACCURACY OF THE METERS AND THE COSISTENCY OF READINGS IN THE FIELD VERSUS THOSE IN THE FACTORY. IF YOU SAW THE IMPROVEMENT YOURSELF THEN MAYBE YOU GOT THE BTUH BOOST BUT NOT AN ACCURATE TOTAL. THE PROOF WILL BE IN THE ELECTRIC BILL (OR METER READING).
I WOULD NOT HESITATE TO BRING IN THE TRANE SPECIALIST. BEING A SERVICE TECH MYSELF, I LIKE WHEN THE SPECIALIST COMES OUT BECAUSE IT WILL GIVE THE CUSTOMER PIECE OF MIND AND IT GIVES ME THE OPORTUNITY TO WATCH HOW THE EXPERTS DO IT. ALSO IF MY COMPANY IS MAKING A MISTAKE, IT GIVES US THE OPORTUNITY TO LEARN AND CORRECT IT FOR THIS JOB AND FUTURE ONES. SOMETIMES WE AS TECHS NEED TO BE HUMBLED. LOOK FOWARD TO HEARING THE RESULTS OF THE LATEST TWEAK. BY THE WAY, WHAT WAS THE TWEAK? ADJUSTING CHARGE?
-
02-24-2008, 07:11 PM #60
Regular Guest
- Join Date
- Mar 2007
- Posts
- 55
The tweaks and hooking up the loose wire seems to have made a significant difference. We've had several cold days recently and the usage has dropped dramatically...On the order of about 40-45kwh per day (at a minimum). Just a couple of days ago, we had our coldest day of the year with the low dropping to -6 and a high of 22 and usage in 24 hours was 180kwh which is a far cry from our previous coldest day when it got down to -3 and a high of 26 and the usage was 235kwh.
Main reason I didn't have them call the Trane specialist is that if the changes the installers made worked, I didn't think there was much point to it. I know that the charge was changed some but the installer made it sound like they made other tweaks too to the heat pump. I wonder if the tweaks made more of a difference or the loose wire?!