    I Came In On This In The Middle And Im Not And Engineer But It Would Seem To Me That Your Electric Heat Is The Source Of Yur Problem. Your Electric Problems Occured When You Started Using 2nd Stage And Aux. You Have 20 Kw Of Electric Heat Which Seems High To Me But Im Not Sure About Your Climate. Your Heating Stages Are All Tied Together As Per The Picture You Submitted. When Ive Done It Before, W1 And W2 Are Wired Through Seperate Outside Stats And Your Output From Your Condenser During Defrost Should Be Connected To W3. Assumming That The Charge Was Properly Weighed In, The Pipe Sizes Are Correct And The Pressures Match The Chart In The Service Facts,the Filters Are Clean Etc, Your Problem Sounds To Be Electric Heat Related. My Old Boss Used To Say "dont Chase Btu's Down Rat Holes" Youll Find That Most Problems Are Very Simple And Have A Way Of Getting Complicated

  2. #54
    Join Date
    Jan 2008
    Posts
    7
    Quote Originally Posted by s012adh View Post
    Well the installer (as well as the president of the company) is coming out next Tuesday to take a look at things. I know according to ARI, my specific unit has an HSPF of 8.75. From the recommendations of other people here, it sounds like the dip switches are set incorrectly. As far as wiring it up for 2 stage vs. 2 step, I don't know if that is the case...Is that something you can gleam off the pictures I took of the wiring? I do currently have the thermostat locking out aux heat above 40 degrees and have tested this and it seems to be working correctly.
    ITS BEEN 10 DAYS AND I WOULD LOVE TO KNOW WHAT HAPPENED. HELLO.....ANYBODY.......HELLO

  3. #55
    Join Date
    Mar 2007
    Posts
    55
    Because of the crappy weather we've been having lately here in Ohio, the installers finally were able to come out today to check things out. One thing that was discovered was that the wire going to one set of heat banks was loose so I was only using the set of banks when aux was on. I know that made a big difference in the temperature output at the register is it shot the temperature up from 100 to 126. If I was only using 1 heat bank and the electric bill was so high, I have to wonder if fixing this could make the electric usage worse...

    They also did some tweaking to the heat pump to get it more inline with factory specs. Before the tweaks, they were showing the BTU output at just over 20,300 (at 32 degrees) and after they tweaked it, the BTU output was 23,200. With the tweaks it raised the COP number to just above 3 and the EER was raised to be 10.2.

    Aside from those 2 changes, they said everything else was in order and correct, including how the dip switches were set. They said the airflow setting (even though it appears to be set to 3.5 tons) is set correctly since they're getting about 1200 cfm. And they said that they always set the aux airflow setting to be lower as it helps to increase comfort.

    In a couple of days, we're supposed to have some pretty cold days again so I'll be able to tell if the changes that were made had any effect whatsoever on the electric usage. Once I am able to determine that, I'll let everyone know my findings.

  4. #56
    Join Date
    Jul 2007
    Location
    Tulsa, OK
    Posts
    846
    All of this info for a residential topic? Pro Forum , you think?

  5. #57
    Join Date
    Aug 2007
    Location
    Northern VA 38 degrees N by 76 degrees W
    Posts
    3,251
    Quote Originally Posted by s012adh View Post
    Because of the crappy weather we've been having lately here in Ohio, the installers finally were able to come out today to check things out. One thing that was discovered was that the wire going to one set of heat banks was loose so I was only using the set of banks when aux was on. I know that made a big difference in the temperature output at the register is it shot the temperature up from 100 to 126. If I was only using 1 heat bank and the electric bill was so high, I have to wonder if fixing this could make the electric usage worse...

    They also did some tweaking to the heat pump to get it more inline with factory specs. Before the tweaks, they were showing the BTU output at just over 20,300 (at 32 degrees) and after they tweaked it, the BTU output was 23,200. With the tweaks it raised the COP number to just above 3 and the EER was raised to be 10.2.

    Aside from those 2 changes, they said everything else was in order and correct, including how the dip switches were set. They said the airflow setting (even though it appears to be set to 3.5 tons) is set correctly since they're getting about 1200 cfm. And they said that they always set the aux airflow setting to be lower as it helps to increase comfort.

    In a couple of days, we're supposed to have some pretty cold days again so I'll be able to tell if the changes that were made had any effect whatsoever on the electric usage. Once I am able to determine that, I'll let everyone know my findings.
    Wow these guys are good they have better BTU outputs in the field than the factory!

  6. #58
    Join Date
    Mar 2007
    Posts
    55
    Quote Originally Posted by second opinion View Post
    Wow these guys are good they have better BTU outputs in the field than the factory!
    I know when they left, they told me that if I wanted them to, at any time they would call a Trane specialist to come down to take a look at things. Is it normal for the heat pump to need "tweaked" to get it optimized? How is it possible to have better numbers out in the field than the factory?

  7. #59
    Join Date
    Jan 2008
    Posts
    7
    Quote Originally Posted by s012adh View Post
    I know when they left, they told me that if I wanted them to, at any time they would call a Trane specialist to come down to take a look at things. Is it normal for the heat pump to need "tweaked" to get it optimized? How is it possible to have better numbers out in the field than the factory?
    I DONT WANT TO PASS JUDGEMENT ON YOUR CONTRACTOR. IF YOU THINK HE DESERVES THE BENEFIT OF THE DOUBT, CONSIDER THE ACCURACY OF THE METERS AND THE COSISTENCY OF READINGS IN THE FIELD VERSUS THOSE IN THE FACTORY. IF YOU SAW THE IMPROVEMENT YOURSELF THEN MAYBE YOU GOT THE BTUH BOOST BUT NOT AN ACCURATE TOTAL. THE PROOF WILL BE IN THE ELECTRIC BILL (OR METER READING).
    I WOULD NOT HESITATE TO BRING IN THE TRANE SPECIALIST. BEING A SERVICE TECH MYSELF, I LIKE WHEN THE SPECIALIST COMES OUT BECAUSE IT WILL GIVE THE CUSTOMER PIECE OF MIND AND IT GIVES ME THE OPORTUNITY TO WATCH HOW THE EXPERTS DO IT. ALSO IF MY COMPANY IS MAKING A MISTAKE, IT GIVES US THE OPORTUNITY TO LEARN AND CORRECT IT FOR THIS JOB AND FUTURE ONES. SOMETIMES WE AS TECHS NEED TO BE HUMBLED. LOOK FOWARD TO HEARING THE RESULTS OF THE LATEST TWEAK. BY THE WAY, WHAT WAS THE TWEAK? ADJUSTING CHARGE?

  8. #60
    Join Date
    Mar 2007
    Posts
    55
    The tweaks and hooking up the loose wire seems to have made a significant difference. We've had several cold days recently and the usage has dropped dramatically...On the order of about 40-45kwh per day (at a minimum). Just a couple of days ago, we had our coldest day of the year with the low dropping to -6 and a high of 22 and usage in 24 hours was 180kwh which is a far cry from our previous coldest day when it got down to -3 and a high of 26 and the usage was 235kwh.

    Main reason I didn't have them call the Trane specialist is that if the changes the installers made worked, I didn't think there was much point to it. I know that the charge was changed some but the installer made it sound like they made other tweaks too to the heat pump. I wonder if the tweaks made more of a difference or the loose wire?!