Page 2 of 10 FirstFirst 123456789 ... LastLast
Results 14 to 26 of 123
    North Carolina
    Just out of curiosity, what is going to keep the compressor from overheating if you drop the suction line size by a quarter of an inch? Unless the manufacturer oversized the line (could happen I guess) it will strain the compressor & it will fail prematurely. Walk up to a unit with an undersized line & you can hear the difference. It sound's like it's working hard even when it shoulden't. (just my opinion)
    SC
    Goodman has recently upped the vapor line requirements. They DO spec them in the installation document. Sometimes it is enough to run PART of the line in the larger size. This is also covered in the installation doc.
    I recently installed a 5 ton Goodman. The new spec requires 1 1/8, the old was 7/8. The parts counter sent 7/8 to the jobsite after I specified 1 1/8. I sent one of my guys to exchange it, and he came back with the same 7/8! The counter guy was cocksure the 7/8 was the correct size.
    Yes, it will run on the smaller size. What will it cost you? Only the future will tell for sure. Some loss in efficiency and compressor life are probabilities.
    Nov 2000
    Eastern PA
    Quote Originally Posted by gevans View Post
    No loss of efficiency or any compressor damage. The only thing a reduced vapor line does is to lessen the capacity of the system.
    ...seek, and ye shall find;..
    Ecclesiastes 10:2 NIV
    Nov 2000
    Eastern PA
    Quote Originally Posted by model m-man View Post
    Your opinion has merit in logic but is not accurate. A smaller suction line decreases capacity but does not raise the teperature of the compressor as the system would have been charged according to parameters including the smaller suction line.
    I'd think "loss of capacity" is directly related to loss "efficiency ".
    Massachusetts
    Quote Originally Posted by TLY View Post
    Well, it must have impacted something in a significant way. That is an increase of 33%. (3/4'' nominal to 1'' nominal) I would be interested to know what problems were solved or what efficiencies were increased by changing this specification.
    Specifications are a funny thing...some say they are of no real significance and some say they are critical...still confused.
    TLY
    Could it be that 1-1/8 is the next size up from 7/8 and if they wanted or needed 10% more, they HAD to move up 33%??????
    Specifications are there for a reason. But those who've been doing this for a while are all well aware that the man's all state that a reduction in line size will only lead to loss of capacity. Some even publish specs for 'undersized lines'.
    Nov 2007
    Quote Originally Posted by RoBoTeq View Post
    By how much is the capacity lessened?
    N.E. Ok.
    Wiithout looking it up i think this is probably real close.
    Check the mfrs. specs,might just be a 3% capacity loss.
    Nov 2007
    Quote Originally Posted by captube View Post
    So does that mean a 4 ton unit will function like a 3.88 ton unit? Also, are sensible and latent cooling capacities equally affected, or is one affected more than the other?
    Thanks,
    TLY
    Nov 2000
    Eastern PA
    I've checked into that and am told that if that were the case that manufacturer's would have to state as much in the charts. It seems that the amount of capacity decrease causes lower power consumption at the same time. More then likely a matter of how much refrigerant is being pushed through the system being less with a smaller line.
    Either way, it is too minimal to calculate in the field.
    Nov 2000
    Eastern PA
    On a 50' line the capacity using 7/8" instead of 1-1/8" is 97% of full capacity.
    So, if a 3 ton unit actually did produce 36,000 Btu of cooling (which they don't), it would only produce 34,920 Btu of cooling using a 7/8" suction line.
    Do not mess with the liquid line though. Big difference between liquid and vapor.
    I'd have thought differently,but I'll accept thtat since you say so.
    Nov 2000
    Eastern PA
    I'm not making this a fact. Just an assumption based on heresay and manufacturer's not addressing it any differently. What you state makes sense as well. Then again, I urge techs to lower indoor airflow to increase latent heat removal which also reduces efficiency.
    Sometimes it's not all about efficiency