Page 1 of 10 12345678 ... LastLast
Results 1 to 13 of 123
    Nov 2007
    1-1/8'' Suction Line
    Goodman GSH130481AA Heat Pump specifications call for a 1-1/8'' suction line size (O.D.). Can an already in place 7/8'' line be used without ANY problems? What problems are possible from an undersized suction line?
    Thanks,
    TLY
    Phoenix Arizona
    usually but not always its ok...Im not sure about goodman but other units have piping charts...
    "If history repeats itself I am so getting a dinosaur"
    Ohio
    Better refer to the sizing charts...if it says you need to use 1 1/8 line then you probably should. Not only for proper opperation, but also for any kind of warranty situation that you may see in the future. And no I am not bashing Goodman, they are great units!
    I need a new signature.....
    Check the mfrs. specs,might just be a 3% capacity loss.
    Nov 2000
    Eastern PA
    That is about it.
    How long is the lineset?
    ...seek, and ye shall find;..
    Ecclesiastes 10:2 NIV
    Massachusetts
    I agree. Know what the load is and if the unit has some excess capacity, you're probably okay. Check the man's specs.
    Nov 2007
    Quote Originally Posted by RoBoTeq View Post
    The lineset is 50 feet.
    Nov 2000
    Eastern PA
    Quote Originally Posted by TLY View Post
    Should not be an issue.
    Nov 2007
    If a suction line is too small will it cause any noise problems or will it only affect efficiency?
    Nov 2000
    Eastern PA
    As long as you are only dealing with vapor, which is all you should be dealing with in that line, I have never come across any sound issues with a smaller suction line.
    Jun 2007
    Metro St. Louis
    Up until recently, Goodman wanted 7/8". For example, in September, the ASZ heat pump I have was spec'd at 7/8". In October, they updated the specs to 1 1/8". I'm not sure why they moved up (Robo might know), but if it was good before, I'm sure it would be fine now. Perhaps not optimal...
    Nov 2007
    Quote Originally Posted by Waterloo View Post
    Well, it must have impacted something in a significant way. That is an increase of 33%. (3/4'' nominal to 1'' nominal) I would be interested to know what problems were solved or what efficiencies were increased by changing this specification.
    Specifications are a funny thing...some say they are of no real significance and some say they are critical...still confused.
    TLY
    By itself, its not much of an impact.
    If all other operating parameters are off alittle, it could make a big difference.