    TRANE gas furnace question

    Hi: I have a customer with a resently install Trane horz, furnace. A 30 year old house with a ICP 2 ton H coil & 3.5 ruud condenser. I want to install a 2.5 or 3 ton evap. can not figure what size drive is on this furnace TUH1B060A9361AA . thanks

  2. #2
    Join Date
    Nov 2006
    Location
    SE Ohio
    Posts
    12,903
    Post Likes
    The "36" in the model number probably means 3 ton drive. However, I'm not a Trane dealer, so that's my best guess.

  3. #3
    Join Date
    Jul 2007
    Location
    Virginia
    Posts
    19,248
    Post Likes
    Quote Originally Posted by deadeye52 View Post
    I want to install a 2.5 or 3 ton evap. can not figure what size drive is on this furnace TUH1B060A9361AA
    At 0.40” wc you will have 1204 cfm. So 3 tons, if the static pressure isn’t any higher and you are shooting for 400 cfm per ton.

    Any idea what kind of static pressure you are dealing with?
    Instead of learning the tricks of the trade, learn the trade.

  4. #4
    Join Date
    Jun 2012
    Location
    Arkansas
    Posts
    1,359
    Post Likes
    Not a Trane dealer, but 60,000 BTU furnaces usually have up to a 3-Ton drive.

  5. #5
    Join Date
    Jun 2014
    Location
    Anderson County, SC
    Posts
    145
    Post Likes
    Dean is correct. The 36 past the BTU rating gives you the drive in a Trane m/n.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •