    ILON 100 problem Please Help!!!!!!

    I am working with an ILON 100 e2 server and I am having a problem with getting some NVE's to update (points stay offline). I can see all the data in question through Lonmaker (non-turbo) so I know it is not a network problem. In addition I see data from other points on the same ILON updating and data passes from the ILON to the controller in question through NVL's. However the NVE's only show offline. I have tried resynchronizing the network in Lonmaker, rebooting the ILON, resynchronizing the ILON, restoring the ILON factory defaults, and just about every combination of the preceding. I have also deleted both the ILON and the controller and recomissioned them. I am assuming there is some setting I am missing which is prevented the polling of the values from this particular device, or possibly a corrupted file on the ILON.

    Please help I am ready to give up on the installed
    device and replace it with a new one.


    Thanks

  2. #2
    Join Date
    Mar 2003
    Location
    NY
    Posts
    2,252
    Post Likes
    I am not sure where you are seeing the 'offline' indication but the first thing I would check is to be sure you do not have a heartbeat and a polling value set in the iLON plug-in, one of them needs to be 0. If both have values the NVE will not update on the network.

  3. #3
    Join Date
    Jan 2008
    Posts
    3
    Post Likes
    Thread Starter

    ILON 100 Problem Clarification

    Thank You for your response.

    I am seeing the values as offline when I view the points through the view-data point section on the ILON's service page. I have the polling value set and the other settings such as heartbeat, min send time, etc set to 0.

  4. #4
    Join Date
    May 2002
    Posts
    9,542
    Post Likes
    You haven't altered the devices that the NVE's are polling?

  5. #5
    Join Date
    Sep 2004
    Location
    SoCal
    Posts
    474
    Post Likes
    Do you have a protocol analyzer to confirm the iLON is in fact polling the NVE's? Have you changed any NVE names? I'd seriously consider upgrading to e3 - you should get an extra for that work!

    lb
    A hundred million nodes - it's a LON story.

  6. #6
    Join Date
    May 2002
    Posts
    9,542
    Post Likes
    CLUE: "I see data from other points on the same ILON updating and data passes from the ILON to the controller in question through NVL's."

  7. #7
    Join Date
    Jan 2008
    Posts
    3
    Post Likes
    Thread Starter

    ILON problem further clarification

    Thank all of you for your responses.

    On further investigation of my problem I found that I can see the 2 controllers
    that do not have NVE's updating only if I use LON1, my PCC Lon Card. If I use LON3, the USB Lon interface, I cannot see these 2 controllers. I am now
    wondering if this is less of an ILON100 problem and more of a conflict between these 2 Lon interfaces.

    I have 8 other nodes on my network and there are no communication problems with these. The NVE's for these update and I can see them using
    both Lon interfaces.

    Thanks Again