Thread: Icp furnace model GNJ100N12D1

  1. #1
    Join Date
    Jan 2008
    Posts
    40
    Post Likes

    Icp furnace model GNJ100N12D1

    Both draft and blower motor run constantly, even with stat off. a/c wont come on unless jumped out. Y to w for power..changed out stat and control board. all safety check out ok..I work on 300 ton chillers at a local university for the past 20 years and not the best on the family furnace. any help wold be great

  2. #2
    Join Date
    Feb 2008
    Location
    Altmar, New York, United States
    Posts
    6,687
    Post Likes
    a/c will run when you jump y and w? will do the burners ignite too? you should get someone more familiar with these units.

  3. #3
    Join Date
    Jan 2008
    Posts
    40
    Post Likes
    Thread Starter
    I have a couple of emails out to friends in the Residential field. I have never come across anything like this. yes the burners come on also. the W was the only hot terminal at the furnace and stat so I just jumped it to y to see if the condenser would run, and it did. maybe a short in the 24 volt ??

  4. #4
    Join Date
    Feb 2008
    Location
    Altmar, New York, United States
    Posts
    6,687
    Post Likes
    if you ask to move this to the tech to tech forum we could go into a little more detail. we aren't allowed to give diy advice and even though you are a tech this is an open forum and the info would be available for any guy to see and use. lets try to get it moved. I will tell you I see a simple issue that you may kick yourself for missing. think of how you lv board and stat work with each other.

  5. #5
    Join Date
    Jan 2008
    Posts
    40
    Post Likes
    Thread Starter
    How do i go about moving this to tech forum..thanks

  6. #6
    Join Date
    Feb 2008
    Location
    Altmar, New York, United States
    Posts
    6,687
    Post Likes
    i reported it and requested but am unsure if i can do or if it needs to be you. click on the little black triangle on the bottom left. you can ask there.

  7. #7
    Join Date
    Jan 2008
    Posts
    40
    Post Likes
    Thread Starter
    thanks, did it

  8. #8
    Join Date
    Feb 2008
    Location
    Altmar, New York, United States
    Posts
    6,687
    Post Likes
    what terminal is the w wire hooked to on the board and the stat?

  9. #9
    Join Date
    Jan 2008
    Posts
    40
    Post Likes
    Thread Starter
    W

  10. #10
    Join Date
    Jan 2008
    Posts
    40
    Post Likes
    Thread Starter
    From furnace strip to stat .R- red wire to r on stat.. W-white wire to w on stat...G-green to g on stat... Y- blue wire to Y on stat and red wire to condenser...C white wire to condenser...NO C ON STAT

  11. #11
    Join Date
    Mar 2013
    Location
    East Concord, NY
    Posts
    22,646
    Post Likes
    sounds like there is a limit open
    Nest is POO!!

  12. #12
    Join Date
    Jan 2008
    Posts
    40
    Post Likes
    Thread Starter
    I will re check the limit and roll out

  13. #13
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Is there a float switch.

    Does new stat have an RC terminal?

  14. #14
    Join Date
    Jan 2008
    Posts
    40
    Post Likes
    Thread Starter
    yes I have a jumper from rh and rc

  15. #15
    Join Date
    Jan 2008
    Posts
    40
    Post Likes
    Thread Starter
    I also just replaced the limit switch and still not working right

  16. #16
    Join Date
    Jan 2008
    Posts
    40
    Post Likes
    Thread Starter
    no float switch

  17. #17
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Time to get the meter out and start tracing out wires.

  18. #18
    Join Date
    Jan 2008
    Posts
    40
    Post Likes
    Thread Starter
    I think that's my next step. thanks

  19. #19
    Join Date
    Jan 2008
    Posts
    40
    Post Likes
    Thread Starter

    ICP Model GNJ100N12D1 Blower won't shut off

    I'm a retired Chiller tech..Ok, my home furnace has me stumped. Had a little water come down exhust vent pipe and the top of the furnace was wet. repaired leak..now the draft and blower motor runs all the time ..Have replace the board twice along with the limit switch and New nest and still not fixed..blowers running even when the stat is in the off position..it will call for heat and cycle but will not run the a/c ..I can jump out the a/c and it will run. took all the 24 volt wires off the board and both blowers still running..HELP I use to think I was a pretty good tech but this has me stumped.

  20. #20
    Join Date
    Jul 2013
    Location
    Harrisburg, PA
    Posts
    436
    Post Likes
    Did you check all the safety limits? There may be one on the blower that's open, causing the problem. You said the furnace lights though? Only a two year tech here.


    Life is 10% what happens to you and 90% how you react.

+ Reply to Thread
Page 1 of 3 123 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •