Thread: Trane Startup noise

  1. #1
    Join Date
    Jan 2008
    Posts
    8
    Post Likes

    Trane Startup noise

    I recently had a Trane XL16i & paired air handler installed.
    When the unit starts up - especially when it is cold - it makes a loud noise for about 5-10 seconds. During normal running it is quiet. The noise is even louder and lasts longer when it goes into defrost mode.

    Unfortunately it is directly below a bedroom window and wakes me every time.

    The dealer replaced the heat pump under warranty because they agreed it was not normal, but the replacement does the same thing. Now they claim the noise is normal. I have seen some attribute it to the reversing valve and others say it is the scrolling compressor.

    Does anyone have any ideas as to the problem or ways to mitigate the problem?

    --Sleepless--

  2. #2
    Join Date
    Jun 2001
    Location
    Louisville, KY
    Posts
    12,855
    Post Likes
    Two likely scenarios...

    Crankcase heater not working or not installed

    -or-

    Overcharged system


    Neither can be fixed by a homeowner.
    Perhaps you should have read the instructions before calling.

  3. #3
    Join Date
    May 2007
    Location
    somewhere between heaven and hell
    Posts
    963
    Post Likes
    Was under bedroom window the only option you had to install it? I try not to install equipment under bedroom windows due to that fact of keeping you up at night but sometimes that may be your option.

  4. #4
    Join Date
    Jan 2008
    Posts
    8
    Post Likes
    Thread Starter
    The previous unit was within a few feet, but it was not as tall and was under an overhang. The old unit - a builder grade unit - did not make any noise other than the normal fan running.

    Does anyone here have experience with the Trane XL16i? If so, is it normal to make a much louder noise on startup and in defrost mode?

    I looked through the installer guide for the unit and did not see a "crankcase heater" mentioned or shown in the illustrated diagram. What would it look like? Is it an option or normally installed? I'm in Maryland, near DC, so we don't get very bad winters.

    The techs and the installation manager (who don't need to look at a map to get to my house by this point..) have checked the pressure every time and indicate it is OK.

  5. #5
    Join Date
    Aug 2007
    Location
    MN
    Posts
    2,686
    Post Likes
    we have installed 4 16i HP's this winter, all quiet on startup, is the lineset touching the rimjoist as it goess through the wall, possibly amplifying the refrigerant flow? I have had that happen on a few 410 installs before, just had to tweak the lineset to remove pressure against the wood, although I would leave any "tweaking" to the contractor, kinked copper gets expensive if you do that yourself .
    You can't fix stupid

  6. #6
    Join Date
    Jan 2008
    Posts
    8
    Post Likes
    Thread Starter
    They used the same lines that the previous unit used after a cleaning and pressure test (allegedly). I know my limitations, so I wouldn't try anything myself, but knowledge is power. If I can suggest this to the contractor and resolve the problem, I am happy.

    The lines go through cinder block, not wood. The noise is definitely from the unit, but I cannot pinpoint where. The techs can place the unit into defrost mode manually and it is really loud then. My understanding is that with heat pumps the defrost mode reverses the flow to use the heat normally directed inside, to the outside to defrost the heat pump. (Please correct me if I'm wrong.) This would then tend to lend credence to the reversing value being the culprit. It is not a pressure type noise though. Although they completely replaced the whole heat pump, it still occurs. I guess it is possible for there to be a batch of bad units/valves..

    What I would really like to do is find someone who has had this model or been around one extensively when the unit would go into defrost mode (or was placed in manually using the circuit board) to find out if they experience this noise as well. If all of them do this, then the cure would be different than if there were bad parts. Not knowing anyone else who has this unit does not give me a basis to compare it to.

  7. #7
    Join Date
    Jul 2006
    Location
    Prata di Pordenone Italy
    Posts
    8,069
    Post Likes
    the 16i is one of tranes most quiet units if it is noisy there is a problem

  8. #8
    Join Date
    Dec 2007
    Location
    Eustis
    Posts
    2
    Post Likes
    If it's a loud piercing kind of noise, the solution is to either pinch or remove the factory process stubs.

  9. #9
    Join Date
    Mar 2004
    Location
    Illinois
    Posts
    6,958
    Post Likes
    I would wager to say a call to Trane would get the desired response

    I have more experience in this field than I care to divulge...(might make me look old ) but I can admit to this...I have had scenarios that I could not figure out ( I know hard to swallow that ) and Trane has never hesitated to schedule a job site visit...

    You paid good money for the system...demand what you paid for.

  10. #10
    Join Date
    Aug 2007
    Location
    Northern VA 38 degrees N by 76 degrees W
    Posts
    5,115
    Post Likes
    Quote Originally Posted by wyliecoyote View Post
    The previous unit was within a few feet, but it was not as tall and was under an overhang. The old unit - a builder grade unit - did not make any noise other than the normal fan running.

    Does anyone here have experience with the Trane XL16i? If so, is it normal to make a much louder noise on startup and in defrost mode?

    I looked through the installer guide for the unit and did not see a "crankcase heater" mentioned or shown in the illustrated diagram. What would it look like? Is it an option or normally installed? I'm in Maryland, near DC, so we don't get very bad winters.

    The techs and the installation manager (who don't need to look at a map to get to my house by this point..) have checked the pressure every time and indicate it is OK.
    What is the model # of the indoor/outdoor equipment?

    Line size and length?

    Did the service company leave you with service tickets showing the refrigerant pressures and temperatures?


    Your unit has a c/c heater from factory.

    How long have you had the system installed, and do we know if it is wired correctly?

  11. #11
    Join Date
    Jan 2008
    Posts
    8
    Post Likes
    Thread Starter

    Sound Samples

    The unit is a Trane XL16i, model 4TWX6, paired with a Trane 4TEE3F air handler.

    The heat pump (entire unit) has been replaced, and the lines have been replaced. They claim the refrigerant levels are correct.

    It continues to make the noises described and it now 'freezes' up occasionally. By this I mean that the thermostat shows that the unit should be running, the heat pump fan is running, but nothing is coming out of the air vents. Checking the air handler I find that the fan is not running the the unit is covered with condensation. I have to kill the power for a while and turn it back on to get it working again.

    The installer is now claiming that all scroll compressors make this noise and said that Copeland engineers said it is 'normal'. I have never heard a heat pump make noises like this before.

    Here are samples the sounds it makes, usually at night, when it comes on.

    http://www.xybertech.com/heatpump/sample1.wma
    http://www.xybertech.com/heatpump/sample2.wma
    http://www.xybertech.com/heatpump/sample3.wma
    http://www.xybertech.com/heatpump/sample4.wma

    ANY help would be appreciated!!

  12. #12
    Join Date
    Mar 2003
    Location
    PA/DE area
    Posts
    1,535
    Post Likes
    Is it a 4TEE fan coil??
    It's NOT the BRAND,it's the company that installs it!!!!!

  13. #13
    Join Date
    Jan 2008
    Posts
    8
    Post Likes
    Thread Starter
    I believe it is.. The air handler complete model number is: 4TEE3F31A1000A

  14. #14
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    42,886
    Post Likes
    Where is the air handler? Attic? If so I bet I know what it is. If not, then I'd wonder about overcharge. Obviously slugging.

    That's an unloading scroll. Nordyne is the only one I know who puts CCH on scrolls. But it could help.

  15. #15
    Join Date
    Jan 2008
    Posts
    8
    Post Likes
    Thread Starter
    The air handler is in the basement about 10 feet from the heat pump, which is outside of course.

  16. #16
    Join Date
    Jun 2001
    Location
    Louisville, KY
    Posts
    12,855
    Post Likes
    Flooded start.

    Hmmm...

    That was my answer last winter.
    Perhaps you should have read the instructions before calling.

  17. #17
    Join Date
    Jan 2008
    Posts
    8
    Post Likes
    Thread Starter
    The unit was replaced since last winter and also moved.

    What does 'Flooded Start' mean? Something I can tell the installer.

    The sounds are not 'normal' as they have tried to tell me? I don't think they are but I wanted people who have installed them to give an opinion..

    THANX!

  18. #18
    Join Date
    May 2007
    Location
    Naples, Fl
    Posts
    889
    Post Likes
    What does 'Flooded Start' mean? Something I can tell the installer


    the refrigerant migrates to the coldest point.

  19. #19
    Join Date
    Jul 2006
    Location
    south carolina
    Posts
    178
    Post Likes
    sounds like a refrigerant migration problem. LLSV mite cure this loud noise on start-up
    Two Hydrogen atoms met one day. One said to the other "I've lost my electron". The second said "Are you sure?" The first said "Yes, I'm positive".

  20. #20
    Join Date
    Jan 2008
    Posts
    8
    Post Likes
    Thread Starter
    I did a search, but could not locate what LLSV stands for..

    Is this noise (sound file links posted previously) something unique to scroll compressors or just Trane scrolls? My understanding is that Trane uses a modified Copeland.

    My installer is big in my area and have had a lot of people look at it. I wont mention their name because I want a resolution not point fingers. They have offered to remove it and let me go with something completely different.

    Is this noise indicative of a Scroll? Should I go with a reciprocating compressor? I just want this nightmare to be over with..

Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •