AI-3 can only be used for 0-10vdc devices, and AI-4 can only be an RTD.
Just leave the zone sensor on AI-4. If you need add another RTD for box discharge temp, you will have to buy a device that gives a 0-10 signal output with the RTD input. Kele makes a device that works