Results 1 to 7 of 7
    Nov 2007
    VMA 1420: Unable to define AI-4 for the Side Loop input
    I am working (actually beating my head in) with HVAC PRO Version 8.07
    I have successfully configured and started up a 1420 VMA as Single Duct with box reheat.
    I also have an additional, non related, reheat coil and valve in a different area.
    I have:
    AO-1 Analog 0-10VDC box heating valve
    AO-2 Analog 0-10VDC separate room heating valve
    AI-1 TE-6700 series Zone Temp Sensor w/
    AI-2 as the Warm Cool Adjust
    AI-3 Unused side loop input
    AI-4 TE-6700 series Room Sensor
    The problem is I can not change the side loop input form AI-3 to AI-4?
    Any ideas on what I am doing wrong?
    Any help would be greatly appreciated – Thanks in advance
    Taxachuesetts
    Quote Originally Posted by BasicCntrl View Post
    I have:
    AI-3 can only be used for 0-10vdc devices, and AI-4 can only be an RTD.
    Just leave the zone sensor on AI-4. If you need add another RTD for box discharge temp, you will have to buy a device that gives a 0-10 signal output with the RTD input. Kele makes a device that works
    Mar 2006
    "Sideloops" in VMAs are a different animal than other ASC's. you have to do it in the QA. That will be the place to try to do what you want. It may/may not be possible.
    Michigan
    IN your Q/A the last question, "seperate control loop" answer yes and select AI to AO. Then go to your inputs, delete AI-4 by opening up the point. Go into your AI-3 called "side loop input" change the AI number from 3 to 4. change the setup to your nickle F or whatever sensor your using. Go into your Params and at the bottom is your sideloop settings.
    You can move any auto assigned AI/BI/BO/AO but where your moving it to must not be used already.
    "Yeah I can figure out whats wrong with it, but you were here first and there isn't room for two, plus it's cold up here, I'll be in the van"
    Nov 2007
    Thank you - keepyoucool2003!
    It Worked!
    Taxachuesetts
    Quote Originally Posted by keepyoucool2003 View Post
    You can change the software but the VMA hardware only supports 0-10vdc on AI-3.
    From the JCI Manual:
    Sideloop (humidity, dew point) (for 1410, 1420, 1430) or Static Pressure (for 1440) AI-3 0-16 VDC
    Supply Air Temperature or Supplemental Heat Temperature
    AI-4 1 K Ni, Si, Pt, or 2.25 K NTC
    Michigan
    Quote Originally Posted by krac View Post
    You need to read closer, your correct, but that's not what we did. We moved the predefined AI-3 "Sideloop Input" to AI-4 by changing the number in the params of that "sideloop input" He already had the sensor attached to AI-4. This is the same way you move predefired AI's BI's BO's that are used in other "standard" applications if your point is not on the predefied point.