    Ideal pressure drop across brazed plate exchangers

    In this case:Aquasnap 30 ton. Im running around 13 drop.

  2. #2
    Join Date
    Oct 2005
    Posts
    921

    Lightbulb

    What does the manufacture call for?

  3. #3
    that sounds about right to me

  4. #4
    Join Date
    Jul 2003
    Location
    Orange County N.Y.
    Posts
    1,176
    Quote Originally Posted by vsba View Post
    In this case:Aquasnap 30 ton. Im running around 13 drop.
    The drop sounds ok but it may have been better if you gave the actual numbers as well as the temperature drop and the approach.

    ...Ron
    Roof Rat

  5. #5
    Join Date
    Jan 2006
    Posts
    20
    Actually I found the strainer full of what i think was flux,(another company just replaced all the 2-way valves with 3-ways). Cleaned it up, now im running 8psi drop and the t116 alarms have stopped.

  6. #6
    Join Date
    Feb 2007
    Posts
    533
    Unless the manufactuer states otherwise I go with a 10 delta P .