Results 1 to 6 of 6
    Jan 2006
    Ideal pressure drop across brazed plate exchangers
    In this case:Aquasnap 30 ton. Im running around 13 drop.
    Oct 2005
    Lightbulb
    What does the manufacture call for?
    that sounds about right to me
    Jul 2003
    Orange County N.Y.
    Quote Originally Posted by vsba View Post
    The drop sounds ok but it may have been better if you gave the actual numbers as well as the temperature drop and the approach.
    ...Ron
    Roof Rat
    Jan 2006
    Actually I found the strainer full of what i think was flux,(another company just replaced all the 2-way valves with 3-ways). Cleaned it up, now im running 8psi drop and the t116 alarms have stopped.
    Feb 2007
    Unless the manufactuer states otherwise I go with a 10 delta P .