    Care 7 with older 80/100

    Can I talk to XL80/100 with care7? Controler is 10 years old(5 pin) connector. I do not have the original program. It is a stand alone control for a boiler room. Thanks for any help.

  2. #2
    Join Date
    Jun 2003
    Location
    Philly, PA
    Posts
    42
    Quote Originally Posted by John Labatt View Post
    Can I talk to XL80/100 with care7? Controler is 10 years old(5 pin) connector. I do not have the original program. It is a stand alone control for a boiler room. Thanks for any help.
    If you don't have the CARE project, you cannot upload the project from any XLxx controllers CPU.

    However, you can connect to the controller with XL Online.
    You'll need the flat 5 pin (B-Port) to DB9 adapter and a Null Modem cable.
    (Honeywell P/N XW584)