    So after running the head pressure up and seeing better TXV metering-did the clog clear permanently? And are we talking oil clog or something else? How has it been performing? Is this on the ALA- N Coil?

  2. #22
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    Quote Originally Posted by Rhinohead View Post
    Damnfoss
    That's funny!
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  3. #23
    Join Date
    Nov 2011
    Location
    St. Louis
    Posts
    7,473
    Post Likes
    Hmmm...we have an inside guy saying it's a run of mischarged bulbs.

    I used the fan disconnect trick on one yesterday - but I thought I was forcing the valve to open a bit...not clearing distributor tubes.
    Is the Religious Right to blame for Christianity's decline?

    They argued that, as the Religious Right became increasingly visible and militant, it became associated with Christianity itself. And if being a Christian meant being associated with the likes of Jerry Falwell, many people—especially political moderates and liberals—decided to simply stop identifying as Christians altogether.

    http://www.theamericanconservative.c...nitys-decline/

  4. #24
    Join Date
    Jan 2011
    Location
    Nashville, TN
    Posts
    39
    Post Likes
    Are they using Sporlan valves? We've had major problems lately with those valves on Rudd units.

  5. #25
    Join Date
    May 2014
    Location
    Ontario
    Posts
    185
    Post Likes
    I think Trane also had this problem about 2 years ago. My owner had 3 changed in like a month and a half..... He said Trane said it was a bad batch of TXV's.

  6. #26
    Join Date
    Jul 2012
    Posts
    2,366
    Post Likes
    How much superheat do we charge the bulb to? Just weigh in 0.00000000000000012 oz?

  7. #27
    Join Date
    Jan 2011
    Location
    Nashville, TN
    Posts
    39
    Post Likes
    The replacement valves they are giving us are Emerson so i beleive they know they have a problem.

  8. #28
    Join Date
    Mar 2011
    Location
    Ohio
    Posts
    23
    Post Likes
    Our bad valves were Danfoss TXV. I believe the replacement bad ones we installed (also failed) were Danfoss. Expecting a shipment tomorrow- it will be interesting to see what brand and how new off the line they are...

  9. #29
    Join Date
    Mar 2006
    Posts
    14
    Post Likes
    Quote Originally Posted by just_opinion View Post
    If it is then that is DUMBEST design I've seen. Cuz you have to bring 2 wrenches AND a TORCH to replace the valve.

    DUMBEST I say
    Then you haven't had to replace a York Commercial TXV that has the 12 or 15 tube distributor as part of the valve. Can't replace the valve without the distributor and all of the lovely distribution tubes interlaced with the 2nd stage identical valve and tubes.....that IMO is THE DUMBEST DESIGN EVER!

  10. #30
    Join Date
    Jan 2011
    Location
    Nashville, TN
    Posts
    39
    Post Likes
    Quote Originally Posted by captaincompressor View Post
    How much superheat do we charge the bulb to? Just weigh in 0.00000000000000012 oz?
    Are u a retard or something? If u dont don't know how to charge a unit then ur a hack and need to gtfo this site.

  11. #31
    Join Date
    Mar 2006
    Posts
    14
    Post Likes
    Quote Originally Posted by SuperPro View Post
    Are u a retard or something? If u dont don't know how to charge a unit then ur a hack and need to gtfo this site.
    I believe he is referring to charging the sensing bulb on the TXV....obviously one cannot charge this bulb in the field as this is done by machines at the manufacturer. I believe his question was rhetorical and funny too...js

  12. #32
    Join Date
    Jan 2011
    Location
    Nashville, TN
    Posts
    39
    Post Likes
    Yes, I believe he was being a SA now that I think about it.

  13. #33
    Join Date
    Jul 2014
    Location
    Georgia
    Posts
    73
    Post Likes
    My local Copeland rep tells me that R-22 change overs require a filter drier right besides the inside coil. He says even if the outside unit has a filter drier inside it, it still requires a additional filter and that 410-a change overs are now a different story about the 2 inline filters being a no-no.
    He goes on to say that many txv's are showing up with a sticky substance clogging up the orifices in the txv caused by small amounts of left over mineral oil or the flushing agent.

    bb

  14. #34
    Join Date
    Jul 2014
    Posts
    12
    Post Likes
    Having some Major issues with TXV's....hearing a lot about leaking evap coils similar to when Lux aire had a huge problem when the first went micro channel....the Rep gave us a line there was a bacteria that caused the leak....so my answer was..let me get this right...the condenser coil got sick on the way here....REALLY believable.....

    got a 30 ton Carrier RTU on a job delivered (only 2 weeks late on a 6 week lead time) the comfort link control locked out right away....circuit A with no gas...piping looked AWFUL.....found a leak at the EVAP...not fun to find on a start up on a Friday....

    Bottom line I think a lot of the manufacturers are having quality control issues due to the rise in demand and lack of supply.

  15. #35
    Join Date
    Jul 2012
    Posts
    2,366
    Post Likes
    Quote Originally Posted by hellbirdman View Post
    My local Copeland rep tells me that R-22 change overs require a filter drier right besides the inside coil. He says even if the outside unit has a filter drier inside it, it still requires a additional filter and that 410-a change overs are now a different story about the 2 inline filters being a no-no.
    He goes on to say that many txv's are showing up with a sticky substance clogging up the orifices in the txv caused by small amounts of left over mineral oil or the flushing agent.

    bb
    mineral oil does not clog txv's.

  16. #36
    Join Date
    Jul 2014
    Location
    Georgia
    Posts
    73
    Post Likes
    Quote Originally Posted by captaincompressor View Post
    mineral oil does not clog txv's.
    Yes but r11 flush and those other bad word cleaners do, if not completely removed. Something happens with the combination of mineral oil and the flushes or just the flushes them selves and poe. I got from a Copeland training class. Tell it to Copeland. It was not my idea. They claim that they get a lot of TXV'S back with gooyie crap in them on 410-a change outs. I never had a problem.

    bb

  17. #37
    Join Date
    Jul 2014
    Location
    Georgia
    Posts
    73
    Post Likes
    Ask your Copeland rep if he likes flushing the system out on converted R-22 line sets. He was not able to tell me what caused the problems in the TXV'S. He only said to add another LL drier before the evap coil to catch it.

  18. #38
    Join Date
    Aug 2011
    Posts
    1,449
    Post Likes
    Not big fan of txv valve just like ECM motor,to many fail for different reason,if u install by the book,purge nitro while braze,dons't mean txv not goona mulfuction !cost more money for customer and make u look bad if it is newly install!have few brand new txv mulfuction before,customer loss all faith on that product and make me look like a fool!

  19. #39
    Join Date
    Jul 2012
    Posts
    2,366
    Post Likes
    "Its hard to stop a trane" lol

  20. #40
    Join Date
    Jan 2008
    Location
    Madison In.
    Posts
    517
    Post Likes
    But can make a good living keep them going

    Sent from my SCH-S738C using Tapatalk

+ Reply to Thread
Page 2 of 11 FirstFirst 123456789 ... LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •