  1. #14
    Hopefully cleancondenser will respond. He is the metasys master. He can help you out.

  2. #15
    Join Date
    Jan 2008
    Location
    Near Philly
    Posts
    514
    Here is a DX9100 Metastat slider setup I have used in the past, it may not be correct for the the slider you are using.
    Measurement Units = 0
    Type of Active Input = 2
    High Range = 7.4
    Low Range = -5
    High Limit = 100
    Low Limit = -10
    Filter Cont = 0
    Limit Diff = 2
    The Rest = 0

  3. #16
    Join Date
    May 2007
    Posts
    50
    Mechdorn
    I was looking at the metastat, product info and this looks like it may be right, anyway it will be a good place to start.

  4. #17
    I am not sure if this would even work...? But-

    How about using TE-6700 series room sensors with the warm cool adjust?

    Might (can) they work somehow with the DX-9100 AI's?

  5. #18
    Join Date
    Jan 2008
    Location
    Colorado
    Posts
    1
    You can use the TE-67NT-1N00. The product cut-sheets will guide you through the install. Both inputs will be passive AI's, as the slider is just a straight potentiometer. Set your desired range on the passive AI and your good. Hope this helps.

  6. #19
    Join Date
    Jun 2001
    Location
    San Diego, CA
    Posts
    1,149
    seems to me the sensors are 1kohm. If the slider is anywhere near this any old passive input would do. Just see what values it gives and plug them into a segment module for your output. If you want setpoint with the slider for for plus/minus add a calc module.

Page 2 of 2 FirstFirst 12

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event