What are the temps inside. Return air db, wb and supply
Hi: I replace a leaking evap. coil in hud house miller heater. Got a "A" coil almost exact dimensions, except its a 3 ton in place of 2.5 ton evap., fit like a glove. Installed new 2.5 ton 410-A condenser. installation paper said. r22= .73 piston, 410-a = .67 piston.
So I went with smaller piston. A little longer line set also. After running 15 minutes had 250/155 at manifold gauges. Only 4 degrees of super heat. 85 degrees outside dry bulb. only 5 degree's diff. off top of condenser fan. Was thinking of changing to smaller piston. any thoughts, thanks.
What are the temps inside. Return air db, wb and supply
The homeowners were leaving on a trip as I finished. indoor dry blub was about 83 degrees, 64 degrees coming from floor registers.
does not sound bad but maybe try to go back and check under normal conditions
Yeh: I'm going back Monday. It will still be around 80 degrees outside. Hope the homeowner doesnt says its cool, but never shuts off. If that's the case , I guess my next move would be to put a smaller piston in evap.
You need to get return wb and charge by target sh. You either overcharged it. Or its your typical hud house low airflow issue.
Sent from my SM-N900V using Tapatalk
Personally, I would have installed a txv on a mismatched unit just to let it take the work out of guessing.
Advice is always free, but keep in mind free does not mean it's always right.
Seeing mismatched units a lot with the wrong fan speed.
need
Indoor Wet Bulb
condenser dry bulb
vapor pressure
vapor lime temp.
if you have a smart ph, down load check and charge
The chart you looked at was from the evap coil, and not the condenser. That chart was for a 3 ton system, not a 2.5 ton. So you have a 3 ton piston in it, but only a 2.5 ton condenser.
Look at condenser to see if it list a piston size, or only TXVs. Take a 59, 63 and 65 piston with you and see which works better if the condenser does list a size.
If you don't know how to charge a piston metered system, then a different piston won't help. Google "How to charge a piston metered system".
https://www.google.com/#q=How+to+cha...em&safe=active
Last edited by hvacrmedic; 06-22-2014 at 10:14 AM.
The space may be to too limited for a trx valve. The system is not over charge, with no frigerant add and long line set. The condenser came with two pistons ( .60 & .61) , they are too small to fit in evaporator receiver. I did buy a .61 from supplier Saturday that will fit. With some of your suggestion, I think I will pull back charge, swap piston. Maybe reuse dryer, then a good evac. Hopefully pressures will look better and super heat will also.
Ah, so you used the 3 ton piston that came with the evap coil. That will over feed the evap when using a 2.5 ton condenser.
FWIW the only part you would see is the bulb.
All the carrier/bryant and trane/AS txv's are factory installed and are inside the cabinet.
maybe spec some equipment with them installed at the factory?
Here you have somebody that was not willing to make a run to the parts house to get the proper part, a teflon ring to make a good seal. They decided to "fix it". Well you can see the results.
Last edited by r-290; 06-22-2014 at 03:43 PM.
Put the smaller piston in and it ran like a champ, thanks for all the help.